Discussion

Consider the following statements about audit instruments.

1. An averaging clamp meter reads low on a distorted current   2. An infrared thermometer needs the emissivity to be set   3. A spot reading is adequate for a varying load

  • A.2 and 3 only are correct
  • B.1 and 3 only are correct
  • C.1 and 2 only are correct
  • D.1, 2 and 3 are all correct statements about audit instruments

Answer: C

Correct answer: 1 and 2 only are correct

Statements 1 and 2 are correct: an averaging meter is calibrated for a sine wave and under-reads a distorted current, so a true RMS instrument is needed wherever drives or electronic loads are present; and an infrared thermometer computes temperature from radiance, so the emissivity setting must match the surface. Statement 3 is wrong - a varying load needs logging over a representative period, since a spot reading captures one moment of it.