For connecting an alternator to the grid, the phase angle between the generated voltage and the voltage of the grid must be ______.

  • A.0°
  • B.45°
  • C.60°
  • D.90°

Answer: A

For connecting an alternator to the grid, the phase angle between the generated voltage and the grid voltage must be 0°, that is the two voltages must be in phase. Along with equal voltage, equal frequency and the same phase sequence, this lets the breaker be closed without a surge of current.

A phase angle of 45°, 60° or 90° would mean a voltage difference across the breaker at the moment of closing, which would cause a large circulating current and a mechanical shock to the machine. So the first option is correct.