Machine-translated by Google. Questions are authored in English.
Top

Instrument Transformers Questions and Answers

Answer: C

Its secondary sees only the low impedance of an ammeter and its leads, so the flux and hence the error are small. A potential transformer works with a nearly open secondary, since a voltmeter draws almost nothing. Everything else about their behaviour follows from that difference.

Please log in or register to report this question.

Answer: D

It is a series device inserted in a circuit whose current is fixed by the load elsewhere. This is the reverse of a power transformer, where the primary current follows the secondary load, and it is the reason an open secondary is so dangerous.

Please log in or register to report this question.

Answer: A

The errors are computed from measured quantities such as the exciting current, the winding impedances and the burden, without reference to any other transformer. It is laborious, which is why comparison against a standard is the usual practice.

Please log in or register to report this question.

Answer: B

The transformer under test and a standard of the same nominal ratio carry the same primary current, and the difference between their secondary currents is measured in magnitude and phase. Both a deflection and a null version of the method exist.

Please log in or register to report this question.

Answer: C

The exciting current is not proportional to the primary current, so the error expressed as a percentage is quite different at ten per cent of rated current from what it is at full load. Accuracy classes accordingly state limits at 5, 20, 100 and 120 per cent of rated current.

Please log in or register to report this question.

36.

A current transformer of ratio 500/5 supplies an ammeter reading 4 A. The primary current is

Answer: D

Correct answer: 400 A

The ratio is \( 500/5 = 100 \), so \[ 4 \times 100 = 400\ \mathrm{A}. \] The secondary reading is multiplied by the ratio, never by the primary rating alone - reading 500 A off a full-scale assumption is the usual error, and the 20 A offered comes from dividing instead of multiplying.

Please log in or register to report this question.

37.

A potential transformer of ratio 11000/110 supplies a voltmeter reading 105 V. The primary voltage is

Answer: A

Correct answer: 10.5 kV

\[ 105 \times \frac{11000}{110} = 105 \times 100 = 10{,}500\ \mathrm{V} = 10.5\ \mathrm{kV}. \] A potential transformer works exactly as a current transformer does in this respect: the instrument reading times the ratio. The system is running slightly below nominal, which is what the 105 V rather than 110 V is telling the operator.

Please log in or register to report this question.

38.

A wattmeter reads 120 W through a 200/5 current transformer and a 6600/110 potential transformer. The power in the primary circuit is

Answer: B

Correct answer: 288 kW

Both ratios multiply the wattmeter reading, since power is the product of current and voltage: \[ 120 \times \frac{200}{5} \times \frac{6600}{110} = 120 \times 40 \times 60 = 288{,}000\ \mathrm{W} = 288\ \mathrm{kW}. \] Applying only one of the two ratios gives 4.8 kW or 7.2 kW, both of which are offered here.

Please log in or register to report this question.

39.

A current transformer has 400 secondary turns and a single primary turn. Its nominal ratio for a five ampere secondary is

Answer: C

Correct answer: 2000/5

A current transformer is a step-up in turns and a step-down in current, so 400 secondary turns against a single primary turn gives a current ratio of 400 to 1. With 5 A in the secondary the primary carries \( 400\times5 = 2000 \) A, and the nominal ratio is written 2000/5. Reading the turns count as the primary rating gives the 400/5 offered.

Please log in or register to report this question.

40.

A current transformer of turns ratio 200 has an exciting current of 2 A referred to the primary while the primary carries 200 A. The ratio error is about

Answer: D

Roughly, the component of the exciting current in phase with the primary is lost from the secondary, so the secondary reproduces only 198 of the 200 amperes and the ratio error is about one per cent negative. This is why turns compensation is applied.

Please log in or register to report this question.

Loading…
Tags: Instrument Transformers Questions and Answers || Instrument Transformers MCQ Questions and Answers || Instrument Transformers GK Questions and Answers || Instrument Transformers GK MCQ Questions || Instrument Transformers Multiple Choice Questions and Answers || Instrument Transformers GK || GK on Instrument Transformers || Electrical Measurements Questions and Answers || Electrical Measurements MCQ Questions and Answers || Electrical Measurements GK Questions and Answers || GK on Electrical Measurements