Answer: B

Being a ratio of two powers it is dimensionless, and a value of four means four kilowatts of cooling for each kilowatt of input. Its reciprocal expressed per ton is the kilowatts per ton figure the industry usually quotes.

Please log in or register to report this question.

3.

A chiller's efficiency expressed as kilowatts per ton is better when the figure is

Answer: C

Correct answer: lower

Kilowatts per ton is power divided by cooling delivered, so it is an inverse measure - less power for the same cooling gives a smaller number. A good centrifugal machine runs at 0.5 to 0.6 kW/TR at full load and a poor one above 1.0. It is the one efficiency figure in this subject that improves as it falls, which is why it is so easily misread.

Please log in or register to report this question.

4.

A chiller quoted at 0.88 kW/TR has a coefficient of performance of about

Answer: D

Correct answer: 4.0

One ton of refrigeration is 3.517 kW of cooling, so \[ \mathrm{COP} = \frac{3.517}{0.88} = 4.0. \] The two figures say the same thing in opposite directions, and the constant 3.517 converts between them: \( \mathrm{COP} = 3.517/(\mathrm{kW/TR}) \). A COP of 4 means four units of heat moved for each unit of electricity, which is possible because the machine moves heat rather than creating cold.

Please log in or register to report this question.

5.

The integrated part load value of a chiller is quoted because a chiller spends most of its life

Answer: A

A machine sized for the hottest afternoon runs at a third or a half of that for most of the season, and its efficiency there may be better or worse than at full load. A single full-load figure therefore misrepresents the annual consumption.

Please log in or register to report this question.

Answer: B

The same evaporator and condenser surface serving a smaller load gives smaller approach temperatures and therefore a smaller lift for the compressor. The gain is lost if the condenser water temperature is held up artificially.

Please log in or register to report this question.

Answer: C

Evaporation in the cooling tower reaches within a few degrees of the wet bulb, which on a humid day is several degrees below the dry bulb and on a dry day much more. The lower condensing temperature reduces the compressor's lift and its power.

Please log in or register to report this question.

Answer: D

Make-up water, blowdown, chemical treatment and the risk of legionella all attach to the tower, along with the tower fan and the condenser pump. Where water is scarce or dear the air-cooled machine wins despite its poorer efficiency.

Please log in or register to report this question.

Answer: A

A rising approach at constant duty says the tubes are fouled or the charge is low, and the compressor must then work against a lower evaporating temperature for the same chilled water. Trending it is the standard chiller health check.

Please log in or register to report this question.

Answer: B

Correct answer: fouled condenser tubes or non-condensable gas in the circuit

The approach is the gap between the condensing refrigerant temperature and the leaving condenser water, and it measures how well heat crosses the tube wall. Fouling adds resistance to that path, and non-condensable gas blankets the tube surface and raises the condensing pressure. Either forces the compressor to work against a higher head, so a rising approach is an early warning of increasing power for the same duty.

Please log in or register to report this question.

Loading…
Tags: Energy Efficiency in HVAC Questions and Answers || Energy Efficiency in HVAC MCQ Questions and Answers || Energy Efficiency in HVAC GK Questions and Answers || Energy Efficiency in HVAC GK MCQ Questions || Energy Efficiency in HVAC Multiple Choice Questions and Answers || Energy Efficiency in HVAC GK || GK on Energy Efficiency in HVAC || Energy Audit Questions and Answers || Energy Audit MCQ Questions and Answers || Energy Audit GK Questions and Answers || GK on Energy Audit