1.

In a two wattmeter method of measuring power in a three-phase circuit, the two wattmeters will show equal readings when the power factor angle φ is equal to

Exam Year(s)

RSMSSB JE - 2025, RSMSSB - 2025,

Answer: D

The two wattmeters read equal when \(\phi = 0^{\circ}\).

In the two wattmeter method with a balanced load, the readings are \(W_{1} = V_{L}I_{L}\cos(30^{\circ} - \phi)\) and \(W_{2} = V_{L}I_{L}\cos(30^{\circ} + \phi)\). They are equal only when \(30^{\circ} - \phi = 30^{\circ} + \phi\), that is at unity power factor, \(\phi = 0\).

At \(\phi = 60^{\circ}\) one wattmeter reads zero, at \(\phi = 90^{\circ}\) the readings are equal and opposite, and at \(\phi = 30^{\circ}\) one reading is twice the other.

Please log in or register to report this question.

2.

During the measurement of power by two-wattmeter method, the total input power, to a three-phase, 440 V motor running at power factor of 0.8, was found to be 25 kW. The readings of wattmeters will be :
[Given : cos−1(0.8) = 36.87°, sin (36.87) = 0.6]

Exam Year(s)

RSMSSB JE - 2025, RSMSSB - 2025,

Answer: C

The readings are 17.9 kW and 7.1 kW.

In the two-wattmeter method the sum of the readings is the total power, and their difference is related to it through the power factor angle:

\[ \begin{aligned} W_{1} + W_{2} &= 25 \\ W_{1} - W_{2} &= \frac{(W_{1} + W_{2})\tan\varphi}{\sqrt{3}} \\ &= \frac{25 \times 0.75}{1.732} \approx 10.83 \end{aligned} \]

Here \(\tan\varphi = 0.6/0.8 = 0.75\). Solving, \(W_{1} \approx 17.9\) kW and \(W_{2} \approx 7.1\) kW.

Equal readings of 12.5 kW occur only at unity power factor. The pairs 20.2 and 4.8, and 10.9 and 14.1, add up to 25 kW but have the wrong difference for a power factor of 0.8.

Please log in or register to report this question.

3.

Given below are two statements :

Statement I : The compensating coil of a low power factor watt meter compensates the effect of the impedance of current coil.
Statement II : The compensating coil of a low power factor watt meter compensates the effect of the impedance of the voltage coil circuit.

In the light of the above statements, choose the most appropriate answer from the options given below :

Exam Year(s)

RSMSSB JE - 2025, RSMSSB - 2025,

Answer: A

The answer is Statement I is false and Statement II is true.

In a low power factor wattmeter the pressure (voltage) coil is usually connected on the load side, so the current coil carries the load current plus the small current of the pressure coil circuit. At low power factor the deflecting torque is small and this extra current causes a noticeable error. A compensating coil, carrying the pressure coil current and wound alongside the current coil so as to oppose it, cancels the field due to that current.

The coil therefore compensates for the effect of the voltage (pressure) coil circuit, as Statement II says, and not for the impedance of the current coil, so Statement I is false.

Please log in or register to report this question.

4.

The wattmeter in general use for power frequency work is of the

Answer: A

Two coils are used, a fixed current coil and a moving pressure coil, and the torque is proportional to the product of their currents. Being a product it gives true power on any waveform and at any power factor, which no single-coil movement can do.

Please log in or register to report this question.

Answer: B

The fixed coil is the current coil, wound with few turns of thick wire and connected in series with the load. The moving coil is the pressure coil, of many turns of fine wire with a series resistance, and is connected across the load.

Please log in or register to report this question.

Answer: C

Averaged over a cycle the torque is proportional to \( V I \cos\phi \), which is exactly the active power. The cosine term is what makes the instrument read power rather than volt-amperes, and why it reads correctly at any power factor.

Please log in or register to report this question.

Answer: D

The rate of change of mutual inductance with angle is made nearly constant by the shaping of the coils, so the deflection is proportional to the power and the divisions are equal. This is in contrast with the moving iron and hot wire movements, whose scales are square law.

Please log in or register to report this question.

Answer: A

The current in the pressure coil must be proportional to the voltage and in phase with it, which needs a circuit whose resistance far outweighs its reactance. Keeping the current small also limits the error it introduces into the current coil reading.

Please log in or register to report this question.

Answer: B

Eddy current damping is ruled out, because a permanent magnet near the coils would distort the very field on which the reading depends. A light vane moving in a closed sector supplies the damping without introducing any magnetic disturbance.

Please log in or register to report this question.

10.

With the pressure coil connected on the load side of the current coil, the wattmeter reads the power in the load plus

Answer: C

The current coil then carries the load current only, and the pressure coil measures the voltage across the load plus the drop in the current coil, so the current coil loss is included. This connection suits a heavy load current at low voltage.

Please log in or register to report this question.

Loading…
Tags: Measurement of Power Questions and Answers || Measurement of Power MCQ Questions and Answers || Measurement of Power GK Questions and Answers || Measurement of Power GK MCQ Questions || Measurement of Power Multiple Choice Questions and Answers || Measurement of Power GK || GK on Measurement of Power || Electrical Measurements Questions and Answers || Electrical Measurements MCQ Questions and Answers || Electrical Measurements GK Questions and Answers || GK on Electrical Measurements