Energy Audit Instruments Questions and Answers

Answer: A

Connected load and actual demand routinely differ by a factor of two, since machines idle, run part-loaded or stand still. That gap is often where the audit's opportunity lies, and it is why the nameplate total is never used as a consumption figure.

Please log in or register to report this question.

42.

An auditor's infrared readings of a steam header vary widely along its length while a contact probe finds it uniform. The explanation is

Answer: B

Correct answer: the surface finish and therefore the emissivity varies

An infrared instrument infers temperature from emitted radiation, and how much a surface emits at a given temperature depends on its finish - bright metal, oxidised metal, paint and lagging all differ greatly. A header that is uniformly hot but variably painted, cleaned or corroded will therefore read as if its temperature varied. The contact probe measures the temperature directly and is telling the truth.

Please log in or register to report this question.

Answer: C

Drives, rectifiers and electronic lighting are now the majority of many installations, and an averaging instrument understates their current substantially. Since the auditor cannot know in advance which loads are distorted, the true rms instrument is used throughout.

Please log in or register to report this question.

Answer: D

Freedom from contact is exactly its advantage and is why it is used, but its accuracy depends wholly on the emissivity assumed and on what the surface reflects. A calibrated contact probe is the more accurate instrument by a wide margin.

Please log in or register to report this question.

45.

Put the steps of measuring the flow in a duct with an anemometer in order.

1. Compute the volume flow from the mean velocity and the area   2. Measure the free cross-sectional area   3. Take readings at several points across the section   4. Average the readings

Answer: A

The area is established first because it is fixed, then the velocity is sampled across the section because it is not uniform, and the mean of those samples is what multiplies the area. A single centre reading overstates the mean appreciably.

Please log in or register to report this question.

Answer: B

Friction at the wall makes the velocity fall to zero there, so the centre-line value exceeds the mean by a tenth or more depending on the flow regime. A traverse of several points, or a factor from a standard, is what corrects it.

Please log in or register to report this question.

Answer: C

One good clamp-on meter serves fifty measuring points over a week, which no permanent installation could justify. A permanent meter gives the continuous record and is generally the more accurate, being properly installed.

Please log in or register to report this question.

Answer: D

A varying load is precisely what a single reading cannot characterise, and the night-time base load is often the finding that pays for the audit. Accuracy and calibration are unaffected, and a flat tariff is an argument against logging rather than for it.

Please log in or register to report this question.

Loading…
Tags: Energy Audit Instruments Questions and Answers || Energy Audit Instruments MCQ Questions and Answers || Energy Audit Instruments GK Questions and Answers || Energy Audit Instruments GK MCQ Questions || Energy Audit Instruments Multiple Choice Questions and Answers || Energy Audit Instruments GK || GK on Energy Audit Instruments || Energy Audit Questions and Answers || Energy Audit MCQ Questions and Answers || Energy Audit GK Questions and Answers || GK on Energy Audit