Energy Efficiency in Lighting Questions and Answers

31.

A 36 W fluorescent tube on a magnetic ballast draws about 46 W at the circuit. The ballast loss as a fraction of the circuit power is about

Answer: B

Correct answer: 22 per cent

\[ \frac{46 - 36}{46} = \frac{10}{46} = 21.7\ \mathrm{per\ cent}. \] Taking the loss against the lamp wattage instead gives 28 per cent, which is offered here. This is why an installation must be counted at circuit watts rather than at the figures marked on the tubes.

Please log in or register to report this question.

32.

A room 10 m by 8 m requires 300 lux. With a utilisation factor of 0.5 and a maintenance factor of 0.8, the total flux needed is

Answer: C

The area is 80 square metres, so 24 000 lumens would suffice at the working plane, and dividing by the product of the two factors, 0.4, gives 60 000 from the lamps. The two factors together double the requirement, which is why they must never be omitted.

Please log in or register to report this question.

33.

For that same room, with luminaires of 4000 lm each, the number required is

Answer: D

Sixty thousand divided by four thousand is fifteen, which would be arranged as three rows of five for uniformity. The arrangement matters as much as the count, since the standard sets a uniformity as well as an average.

Please log in or register to report this question.

Answer: A

Correct answer: over-lighting, and an opportunity to remove or dim luminaires

Two and a half times the required illuminance is energy spent on light nobody needs, and it can be recovered by removing lamps, dimming, or reducing the maintained level at the next relamping. Note that a design allows some margin for depreciation, but not a margin of this size.

Please log in or register to report this question.

Answer: B

Correct answer: 80 per cent of that room's lighting energy

\[ \frac{10-2}{10} = 80\ \mathrm{per\ cent}. \] Eight of the ten hours are lit with nobody present, and the sensor removes them. This is why stores, washrooms and meeting rooms are where sensors pay, and why fitting one in a continuously occupied space saves nothing.

Please log in or register to report this question.

36.

Removing one tube in three from an over-lit office of 300 twin fittings, each tube taking 46 circuit watts and running 2500 hours, saves about

Answer: C

Two hundred tubes removed at 46 watts is 9.2 kilowatts, and over 2500 hours that is 23 000 units. The remaining fittings should be checked to confirm the illuminance still meets the standard and the uniformity is acceptable.

Please log in or register to report this question.

37.

A luminaire whose diffuser has become dirty enough to absorb 30 per cent of the output is delivering, per watt consumed,

Answer: D

Correct answer: 70 per cent of its original light

Thirty per cent of the output is absorbed by the dirt, so seventy per cent emerges - while the power drawn is unchanged. The effective efficacy of the installation has therefore fallen by nearly a third, which is what a cleaning programme recovers for the cost of the labour.

Please log in or register to report this question.

38.

Match the quantity with its unit.

1. Luminous flux   2. Illuminance   3. Luminous efficacy

P. Lumens per watt   Q. Lumen   R. Lux

Answer: A

Correct answer: 1-Q, 2-R, 3-P

Three quantities and three units. Luminous flux is measured in lumens, the total light emitted. Illuminance is measured in lux, the flux arriving per square metre. And efficacy is lumens per watt, the flux obtained per unit of electrical power - the figure of merit for a lamp.

Please log in or register to report this question.

39.

Match the measure with what it reduces.

1. Occupancy sensor   2. Electronic ballast   3. Light-coloured decoration

P. The flux needed for the same illuminance   Q. The hours of operation   R. The circuit watts per lamp

Answer: B

Correct answer: 1-Q, 2-R, 3-P

Three measures acting on three different terms of the same product. A sensor reduces the hours of operation. An electronic ballast reduces the circuit watts per lamp. And light decoration raises the utilisation factor, so less flux is needed for the same illuminance. Energy is hours times watts, and the third measure reduces how many lamps are required at all.

Please log in or register to report this question.

40.

Put the steps of a lighting audit in order.

1. Measure the illuminance at the working plane   2. Compare against the standard for the task   3. Record the lamp types, wattages and hours   4. Identify over-lighting, relamping and control opportunities

Answer: C

Correct answer: 3, 1, 2, 4

Recording what is installed and how long it runs comes first, since the energy cannot be computed without it. The illuminance is then measured, compared against the standard for the task, and the opportunities identified from the gap between what is provided and what is needed.

Please log in or register to report this question.

Loading…
Tags: Energy Efficiency in Lighting Questions and Answers || Energy Efficiency in Lighting MCQ Questions and Answers || Energy Efficiency in Lighting GK Questions and Answers || Energy Efficiency in Lighting GK MCQ Questions || Energy Efficiency in Lighting Multiple Choice Questions and Answers || Energy Efficiency in Lighting GK || GK on Energy Efficiency in Lighting || Energy Audit Questions and Answers || Energy Audit MCQ Questions and Answers || Energy Audit GK Questions and Answers || GK on Energy Audit