If I1 and I2 are currents flowing from the secondary of CT1 and CT2 in pilot wires respectively and n0 and N are number of turns of operating coil and restraining coil respectively in differential protection scheme, then which of the following is correct ?

  • A.\(\frac{n_{0}}{N} = \frac{I_{1} - I_{2}}{\frac{I_{1} + I_{2}}{2}}\)
  • B.\(n_{0} \times N = (I_{1} - I_{2}) \times \left(\frac{I_{1} + I_{2}}{2}\right)\)
  • C.\(n_{0} \times N = (I_{1} - I_{2}) \times 2(I_{1} + I_{2})\)
  • D.\(\frac{n_{0}}{N} = \frac{\frac{I_{1} + I_{2}}{2}}{I_{1} - I_{2}}\)

Answer: D

The correct relation is \(\frac{n_{0}}{N} = \frac{(I_{1} + I_{2})/2}{I_{1} - I_{2}}\).

In a biased (percentage) differential relay, the operating coil carries the difference current \(I_{1} - I_{2}\), and the restraining coil, connected at the midpoint of the pilot wires, carries the average current \(\frac{I_{1} + I_{2}}{2}\). At the operating threshold the two sets of ampere-turns balance:

\[ \begin{aligned} n_{0}(I_{1} - I_{2}) &= N\,\frac{I_{1} + I_{2}}{2} \\ \frac{n_{0}}{N} &= \frac{(I_{1} + I_{2})/2}{I_{1} - I_{2}} \end{aligned} \]

The first option is this ratio turned upside down. The two options with \(n_{0} \times N\) multiply the turns, which does not come from balancing ampere-turns.