According to Indian Electricity Rule-48, the maximum permissible value of leakage current that should not exceed beyond _______ times of full load current.

  • A.1/1000
  • B.1/2000
  • C.1/5000
  • D.1/10000

Answer: C

The leakage current must not exceed 1/5000 of the full load current.

Rule 48 of the Indian Electricity Rules, 1956 deals with the insulation of installations: the insulation resistance between conductors and earth must be such that the leakage current does not exceed one five-thousandth of the maximum current supplied to the installation. With a full load current of 50 A, for example, the leakage may be at most 10 mA.

1/1000 and 1/2000 would allow far more leakage than the rule permits, and 1/10000 is stricter than the rule requires.