Measuring power factor at a feeder is worthwhile in an audit because a poor factor

  • A.shortens the life of the metering equipment
  • B.raises the current for the same useful power
  • C.reduces the voltage available at the load
  • D.increases the harmonic content of the current

Answer: B

Correct answer: raises the current for the same useful power

\[ I = \frac{P}{\sqrt{3}\,V\cos\phi}, \] so a low power factor means more current for the same real power. That extra current heats the cables and the transformer, consumes capacity that could carry useful load, and attracts a penalty on most tariffs. It does not reduce the voltage at the load appreciably, nor cause harmonics - though harmonics do reduce the overall power factor.