A load of 500 kW at a power factor of 0.8 imposes an apparent demand of

  • A.400 kVA
  • B.500 kVA
  • C.550 kVA
  • D.625 kVA

Answer: D

Correct answer: 625 kVA

Apparent power is the real power divided by the power factor: \[ \frac{500}{0.8} = 625\ \mathrm{kVA}. \] The network must be sized for the 625 kVA, not the 500 kW, because it is the current that heats the conductors - which is exactly why demand is billed in kVA rather than kW.