A metering core and a protection core are often provided on the same current transformer because

  • A.their requirements at fault current are opposite
  • B.one core alone could not carry the ampere-turns needed by both circuits
  • C.the two circuits must be electrically isolated from one another
  • D.the protection relay operates at a different frequency from the meter

Answer: A

Metering wants early saturation to protect the instruments and high accuracy at normal current; protection wants no saturation until far above rated current and accepts a looser ratio. No single core can do both, so two cores share one primary conductor.

No comment is present. Be the first to comment.