A protection current transformer rated 500/1 has an accuracy limit factor of 20. It reproduces the primary current faithfully up to

  • A.25 kA
  • B.10 kA
  • C.500 A
  • D.20 A

Answer: B

Twenty times the rated primary current is ten kiloamperes, at which the secondary carries twenty amperes. Beyond that the core saturates and the relay would see less than the true fault current, which is why the factor must exceed the largest fault the scheme must clear.