In the given figure, the generator is delivering 1.0 pu power to infinite bus (V = 1 pu), with the generator terminal voltage Vt = 1 pu. What is the power angle?

Single line diagram: generator with X'd = 0.25 pu and terminal voltage Vt, a transformer j0.1, two parallel lines j0.5 each, and an infinite bus of voltage 1 angle 0

  • A.\(35.5^\circ\)
  • B.\(31.5^\circ\)
  • C.\(25.5^\circ\)
  • D.\(20.5^\circ\)

Answer: D

The power angle asked for is the angle of the generator terminal voltage \(V_t\) ahead of the infinite bus. The reactance between them is the transformer in series with the two parallel lines of j0.5 each.


\[ X = 0.1 + \frac{0.5}{2} = 0.35\ \text{pu} \]


\[ \begin{aligned} P = \frac{V_tV}{X}\sin\delta \\ &= \frac{1 \times 1}{0.35}\sin\delta \\ &= 1 \Rightarrow \sin\delta = 0.35 \end{aligned} \]


\[ \delta = 20.5^\circ \]


The generator reactance of 0.25 pu would only be used for the angle of the internal voltage behind it, so it is not needed here. The answer is option D.