Machine-translated by Google. Questions are authored in English.
Top

Discussion

A refrigeration system based on reverse Carnot cycle operates between −30 °C and 20 °C. The refrigeration capacity of the system is 70 kW. Heat rejected at the condenser to atmosphere (hot reservoir), in kW, is nearest to

  • A.84.40
  • B.14.41
  • C.186.67
  • D.116.67

Answer: A

The heat rejected is about 84.40 kW.

A reversed Carnot cycle must use absolute temperatures: \(T_{L} = 243\) K and \(T_{H} = 293\) K.

\[ \begin{aligned} COP &= \frac{T_{L}}{T_{H} - T_{L}} = \frac{243}{50} = 4.86 \\ W &= \frac{70}{4.86} = 14.40\ \text{kW} \\ Q_{H} &= Q_{L} + W = 84.40\ \text{kW} \end{aligned} \]

14.41 kW is the compressor work, not the heat rejected. 116.67 kW is what the work comes to if the temperatures are left in degrees Celsius (COP = 30/50 = 0.6), and 186.67 kW is 70 plus that wrong work. Heat rejected must always be the refrigeration load plus the work input.

No comment is present. Be the first to comment.
Loading…

Post your comment

Please log in or register to post a comment.