A factory draws an apparent power of 300kVA at lagging power factor of 0.65. The active power drawn by the factory is:

  • A.285 kW
  • B.228 kW
  • C.185 kW
  • D.195 kW

Answer: D

The active power is 195 kW.

Active power is apparent power multiplied by the power factor.

\[ P = 300 \times 0.65 = 195\ \text{kW} \]

228 kW is the reactive power, \(300 \sin\phi = 300 \times 0.76\), given in kVAR rather than kW, and 285 and 185 kW correspond to no standard calculation from these figures.

No comment is present. Be the first to comment.