A surge comparison test on a machine winding detects

  • A.turn-to-turn faults by comparing the responses of two phases
  • B.the insulation resistance between winding and earth
  • C.the mechanical unbalance of the rotor at rated speed
  • D.the efficiency of the machine at its rated load

Answer: A

Correct answer: turn-to-turn faults by comparing the responses of two phases

A steep-fronted surge is applied to two nominally identical windings and their waveforms superimposed. Identical windings give identical traces; a single shorted turn changes the inductance enough to separate them visibly. This is one of the few tests that finds a turn-to-turn fault, which a resistance or insulation measurement will miss entirely.

No comment is present. Be the first to comment.