In a 3-φ controller bridge rectifier, the maximum conduction of each thyristor is :

  • A.90°
  • B.120°
  • C.180°
  • D.60°

Answer: B

Each thyristor conducts for at most 120°.

In a three-phase fully controlled bridge rectifier, two thyristors conduct at any time, one from the upper group and one from the lower group. A new thyristor is fired every 60°, and each one stays in conduction for two of these intervals, 120° of each cycle, when the load current is continuous.

60° is the interval between successive firings, not the conduction period. 180° is the conduction angle of switches in a 180°-mode inverter or of a diode in a single-phase circuit, and 90° does not apply to the three-phase bridge.