A star-star connected transformer without a delta or tertiary winding suffers from

  • A.an excessive phase shift between primary and secondary
  • B.a very much larger leakage reactance than other connections
  • C.distortion of the phase voltages by triple harmonics
  • D.an inability to supply any unbalanced load at all

Answer: C

Correct answer: distortion of the phase voltages by triple harmonics

The magnetising current contains a strong third harmonic, and in a star-star connection with no delta winding and no neutral path that harmonic current cannot circulate. It is therefore forced into the flux instead, and the phase voltages are distorted by a large third harmonic. A delta tertiary provides the circulating path and cures it.