Match the connection with its property.

1. Delta-star   2. Delta-delta   3. Star-star without tertiary

P. No phase shift and can run open delta   Q. Thirty degree phase shift   R. Liable to harmonic voltage distortion

  • A.1-Q, 2-P, 3-R
  • B.1-P, 2-Q, 3-R
  • C.1-R, 2-P, 3-Q
  • D.1-Q, 2-R, 3-P

Answer: A

Correct answer: 1-Q, 2-P, 3-R

Each connection has its characteristic property. Delta-star introduces the 30 degree phase shift between line voltages, which is why vector groups must match when transformers are paralleled. Delta-delta gives no shift and can continue in open delta on two units if one fails. Star-star without a tertiary has no path for triple harmonic currents, so its phase voltages are distorted.