A three-phase transformer bank consisting of three single-phase transformers is used to step down the voltage of a three-phase, 6600 V transmission line. If the primary line current is 10 A, calculate the secondary line voltage for the star/delta connection. The turns ratio is 12.

  • A.3.175 V
  • B.31.75 V
  • C.317.55 V
  • D.0.3175 V

Answer: C

The primary is star connected on a 6600 V line, so the primary phase voltage is


\[ V_{1ph} = \frac{6600}{\sqrt{3}} = 3810.5\ \text{V} \]


The turns ratio of each single phase transformer is 12, so the secondary phase voltage is


\[ V_{2ph} = \frac{3810.5}{12} = 317.5\ \text{V} \]


In a delta secondary the line voltage equals the phase voltage, so the secondary line voltage is 317.5 V, which is the 317.55 V of the options. The primary current of 10 A is not needed for the voltage. The other values are 10, 100 and 1000 times off. The answer is option C.