Energy Efficient Building Design Questions and Answers

Answer: A

Every degree of set point relaxation in summer cuts the cooling hours and the load appreciably, and in a naturally ventilated building it may remove the plant's operation altogether for weeks. It costs nothing but the acceptance.

Please log in or register to report this question.

42.

A wall of total thermal resistance 0.5 m\( ^2 \)K/W has a U-value of

Answer: B

Correct answer: 2.0 W/m2K

\[ U = \frac{1}{R} = \frac{1}{0.5} = 2.0\ \mathrm{W/m^2K}. \] The U-value and the total resistance are simple reciprocals, so improving a wall means adding resistance and watching the U-value fall - with diminishing returns, since each further increment of resistance buys less.

Please log in or register to report this question.

43.

Adding 50 mm of insulation of conductivity 0.04 W/mK to that wall raises its resistance to

Answer: C

Correct answer: 1.75 m2K/W

The insulation contributes \[ R = \frac{t}{k} = \frac{0.05}{0.04} = 1.25\ \mathrm{m^2K/W}, \] and resistances in series add: \( 0.5 + 1.25 = 1.75 \). The U-value falls from 2.0 to 0.57, so 50 mm of insulation has removed more than seventy per cent of the heat loss through that wall.

Please log in or register to report this question.

44.

A wall of 100 m\( ^2 \) and U-value 2.0 W/m\( ^2 \)K with 15 \( ^\circ \)C across it conducts

Answer: D

Correct answer: 3000 W

\[ Q = UA\Delta T = 2.0 \times 100 \times 15 = 3000\ \mathrm{W}. \] The same wall insulated to the 1.75 resistance of the previous item would conduct 857 W instead, which is the whole case for insulation expressed in one comparison.

Please log in or register to report this question.

45.

Glazing of 20 m\( ^2 \) with a solar heat gain coefficient of 0.4 under 500 W/m\( ^2 \) of incident radiation admits

Answer: A

Correct answer: 4000 W

\[ Q = A \times \mathrm{SHGC} \times I = 20 \times 0.4 \times 500 = 4000\ \mathrm{W}. \] Note how this compares with the 3000 W conducted through 100 square metres of uninsulated wall - a fifth of the area admits more heat, which is why glazing rather than opaque fabric usually governs a cooling load.

Please log in or register to report this question.

46.

Replacing that glazing with a coefficient of 0.25 reduces the admitted gain to

Answer: B

The gain falls in proportion to the coefficient, so 500 times 20 times 0.25 is 2.5 kilowatts, a reduction of 1.5. External shading achieving the same reduction would usually cost less and also improve the daylight quality.

Please log in or register to report this question.

47.

A facade of 200 m\( ^2 \) gross wall area carrying 70 m\( ^2 \) of glazing has a window to wall ratio of

Answer: C

Correct answer: 35 per cent

\[ \frac{70}{200} = 0.35. \] Thirty-five per cent is a moderate figure for a commercial facade. It is taken against the gross wall area including the glazing, so dividing by the opaque area alone would give 54 per cent - a different quantity and not the one the codes define.

Please log in or register to report this question.

48.

An indoor illuminance of 300 lux under an outdoor illuminance of 15 000 lux gives a daylight factor of

Answer: D

Three hundred divided by fifteen thousand is 0.02, that is two per cent, which is a reasonable figure for a side-lit room away from the window. Five per cent or more would be a well daylit space needing no electric light in the day.

Please log in or register to report this question.

49.

A room with a window head 2.5 m above floor level can be daylit usefully to a depth of about

Answer: A

Correct answer: 5 m

The usual rule is that daylight penetrates usefully to about twice the height of the window head above the floor, so \[ 2 \times 2.5 = 5\ \mathrm{m}. \] It is the head height rather than the window area that governs, which is why a tall narrow window daylights a room more deeply than a wide low one of the same area.

Please log in or register to report this question.

50.

A roof of 500 m\( ^2 \) at U-value 1.2 W/m\( ^2 \)K under 20 \( ^\circ \)C of difference conducts

Answer: B

Correct answer: 12 kW

\[ Q = UA\Delta T = 1.2 \times 500 \times 20 = 12{,}000\ \mathrm{W}. \] A roof is usually the largest single element of the envelope and receives the strongest solar radiation, so it repays insulation more than any other surface - and is generally the easiest to insulate.

Please log in or register to report this question.

Loading…
Tags: Energy Efficient Building Design Questions and Answers || Energy Efficient Building Design MCQ Questions and Answers || Energy Efficient Building Design GK Questions and Answers || Energy Efficient Building Design GK MCQ Questions || Energy Efficient Building Design Multiple Choice Questions and Answers || Energy Efficient Building Design GK || GK on Energy Efficient Building Design || Energy Conservation and Management Questions and Answers || Energy Conservation and Management MCQ Questions and Answers || Energy Conservation and Management GK Questions and Answers || GK on Energy Conservation and Management