Circuit Breakers Questions and Answers

1.

Primary function of a circuit breaker is :

Exam Year(s)

RSMSSB JE - 2025, RSMSSB - 2025,

Answer: A

The primary function of a circuit breaker is to protect the circuit from overloading and faults.

A circuit breaker is a switch that can make and break the circuit under normal conditions and, crucially, interrupt the large currents of an overload or short circuit, isolating the faulty section before the equipment is damaged.

It does not energise the relay; the relay senses the fault and energises the breaker's trip coil. Measuring fault current is done by current transformers and relays, and raising voltage is the job of a transformer.

Please log in or register to report this question.

2.

In fault current, d.c. component is Idc and maximum a.c. current is Im then asymmetrical breaking current is given by,

Exam Year(s)

RSMSSB JE - 2025, RSMSSB - 2025,

Answer: B

The asymmetrical breaking current is \(\sqrt{I_{dc}^{2} + \left(\frac{I_{m}}{\sqrt{2}}\right)^{2}}\).

The asymmetrical breaking current is the rms value of the total current at the instant the contacts separate. That current is the sum of a dc component \(I_{dc}\) and an ac component whose rms value is \(I_{m}/\sqrt{2}\). The rms value of a dc plus a sinusoid adds in squares:

\[ \begin{aligned} I_{ac} &= \frac{I_{m}}{\sqrt{2}} \\ I_{asymm} &= \sqrt{I_{dc}^{2} + I_{ac}^{2}} \end{aligned} \]

Adding the two components directly overstates the rms value. Leaving out the square root gives a quantity in amperes squared, and taking the root of the plain sum has the wrong units as well.

Please log in or register to report this question.

3.

Given below are two statements :

Statement I : Air blast circuit breaker is useful for low magnitude current extinction.
Statement II : Minimum oil circuit breaker should be used up to 220 kV voltage level.

In the light of the above statements, choose the most appropriate answer from the options given below.

Exam Year(s)

RSMSSB JE - 2025, RSMSSB - 2025,

Answer: C

The answer is Statement I is false but Statement II is true.

Statement I is false: an air blast breaker's extinguishing power is the same whatever the current. When it interrupts a small current, such as the magnetising current of an unloaded transformer, the arc is cut off before current zero (current chopping), causing high overvoltages. It is suited to interrupting large currents at high voltage quickly, not to low-magnitude currents.

Statement II is true: minimum oil breakers, which use a small quantity of oil only for arc quenching, are used for medium and high voltages up to about the 220 kV level; above that, air blast and SF6 breakers take over.

Please log in or register to report this question.

Answer: D

The rated breaking capacity equals the product of rated symmetrical breaking current and rated voltage.

The breaking capacity of a circuit breaker is stated in MVA and is based on the rms value of the symmetrical (ac) component of the current it can interrupt at its rated voltage. For a three phase breaker the product carries the factor √3: breaking capacity = √3 × rated voltage × rated symmetrical breaking current.

The other options are less precise or wrong. 'Breaking current' without 'symmetrical' leaves out which component is meant, and the fault voltage is not the basis of the rating. 'Twice the rated current and voltage' describes no standard rating.

Please log in or register to report this question.

Loading…
Tags: Circuit Breakers Questions and Answers || Circuit Breakers MCQ Questions and Answers || Circuit Breakers GK Questions and Answers || Circuit Breakers GK MCQ Questions || Circuit Breakers Multiple Choice Questions and Answers || Circuit Breakers GK || GK on Circuit Breakers || Switchgear and Protection Questions and Answers || Switchgear and Protection MCQ Questions and Answers || Switchgear and Protection GK Questions and Answers || GK on Switchgear and Protection