Cold store load breakdown for 40 tonnes of respiring produce.
| Load component | Value (kW) | Share |
|---|---|---|
| Product pull-down over 24 h | 37.0 | 86 per cent |
| Respiration | 1.8 | 4 per cent |
| Transmission | 1.4 | 3 per cent |
| Infiltration | 2.6 | 6 per cent |
Which component dominates during steady holding once the produce is cold?
Answer: C
Correct answer: The three continuous loads
Once the produce is at temperature the product pull-down load ceases entirely - it is a transient, present only while the produce is being cooled. What remains is respiration at \( 1.8 \) kW, transmission at \( 1.4 \) kW and infiltration at \( 2.6 \) kW, a continuous total of about \( 5.8 \) kW.
The table therefore describes two quite different duties: a peak of \( 42.8 \) kW during pull-down and a holding load of \( 5.8 \) kW thereafter. Sizing on the holding load alone would leave the plant unable to pull down; sizing on the peak alone leaves it cycling inefficiently for most of its life.