Machine-translated by Google. Questions are authored in English.
Top

Instrument Transformers Questions and Answers

Answer: A

Correct answer: increasing the length of the secondary leads

Longer leads mean more resistance and therefore more burden, which increases both the ratio and the phase angle error - as the earlier burden items show, the effect goes as the square of the secondary current. The other three all reduce the errors: a better core needs less magnetising current, removing an unused instrument lightens the burden, and turns compensation cancels the ratio error at the working point.

Please log in or register to report this question.

62.

An operator finds a wattmeter reading low on a circuit metered through a current transformer whose secondary leads are long and thin. The likely explanation is

Answer: B

Long thin leads impose a substantial burden, which raises the core flux and the exciting current and so makes the secondary current fall further short of the nominal ratio. Shorter or thicker leads, or a one ampere secondary, is the remedy.

Please log in or register to report this question.

Answer: C

Beyond the accuracy limit the core saturates and the secondary current no longer follows the primary, so the relay sees far less than the true fault current. The accuracy limit factor must be chosen to exceed the largest fault the scheme has to clear.

Please log in or register to report this question.

Answer: D

For an ammeter direction does not matter, but a wattmeter, an energy meter or a directional relay must know the sense of the current relative to the voltage. The marks establish which secondary terminal corresponds to which primary terminal at each instant.

Please log in or register to report this question.

Answer: A

One element's torque reverses, so instead of the sum of the two readings the meter registers their difference. On a balanced load at unity power factor that would give nearly zero, which is a common sign of a reversed connection in the field.

Please log in or register to report this question.

Answer: B

The class number is the limit on the ratio error at rated current with the stated burden, in this case half of one per cent. A separate table gives the corresponding limit on the phase angle, in minutes, and wider limits at fractions of rated current.

Please log in or register to report this question.

Answer: C

The primary is the conductor itself, so there is nothing to wind and nothing to insulate. The cable must nevertheless be disconnected at one end to thread it through, unless a split core clamp type is used, which is the arrangement of a clip-on ammeter.

Please log in or register to report this question.

Answer: D

The split core lets the instrument be applied without breaking the circuit, which is its whole purpose. The joint in the magnetic path introduces reluctance and so a larger error than a solid core, which is the price of the convenience.

Please log in or register to report this question.

69.

The reason a current transformer core is often made of nickel iron alloy rather than ordinary silicon steel is that it has

Answer: A

The exciting current at the low flux densities of normal service is what determines the error, and nickel iron alloys need far less of it. They saturate at a lower flux density than silicon steel, which for a metering core is a positive advantage.

Please log in or register to report this question.

70.

Comparing the burden of an ammeter with that of the leads in a five ampere secondary circuit of twenty metres, the leads

Answer: B

Twenty metres out and back of two and a half square millimetre cable is around a third of an ohm, which at five amperes is more than eight volt-amperes, comparable with or larger than the ammeter itself. Lead burden is routinely the dominant term.

Please log in or register to report this question.

Loading…
Tags: Instrument Transformers Questions and Answers || Instrument Transformers MCQ Questions and Answers || Instrument Transformers GK Questions and Answers || Instrument Transformers GK MCQ Questions || Instrument Transformers Multiple Choice Questions and Answers || Instrument Transformers GK || GK on Instrument Transformers || Electrical Measurements Questions and Answers || Electrical Measurements MCQ Questions and Answers || Electrical Measurements GK Questions and Answers || GK on Electrical Measurements