Performance of Transmission Lines Questions and Answers

1.

In the case of series compensation, if 75% of the compensation is used, the maximum power transferred will ______.

Exam Year(s)

DSSSB AE - 2023,

Answer: C

The maximum power that a line can transfer is inversely proportional to its reactance. A series capacitor reduces the net reactance, and with a degree of compensation \(k\)


\[ \begin{aligned} X_{net} \\ &= X(1 - k),\qquad P_{max} \propto \frac{1}{X(1 - k)} \end{aligned} \]


For 75 per cent compensation, \(k = 0.75\):


\[ \frac{P'_{max}}{P_{max}} = \frac{1}{1 - 0.75} = 4 \]


So the maximum power transferred becomes four times the original. The power would be doubled at 50% compensation. The answer is option C.

Please log in or register to report this question.

2.

In FACTS, the letter 'F' stands for ______.

Exam Year(s)

DSSSB AE - 2023,

Answer: C

FACTS stands for Flexible AC Transmission Systems: power electronic controllers such as the static VAR compensator, the TCSC and the STATCOM that control voltage, impedance and phase angle so that a line can carry more power in a controllable way. The letter F is for Flexible, not for forward, fixed or finite. The answer is option C.

Please log in or register to report this question.

3.

Which of the following is NOT an FACT (Flexible AC Transmission) device?

Exam Year(s)

DSSSB AE - 2023,

Answer: D

FACTS devices are power electronic controllers for AC transmission systems: shunt compensators (the static VAR compensator and STATCOM), series compensators (TCSC and SSSC), and combined controllers such as the unified power flow controller (UPFC). A DC-DC converter changes one DC voltage level to another, and it is used in drives and power supplies, not as a FACTS controller of an AC line. The answer is option D.

Please log in or register to report this question.

4.

The thyristor-controlled reactor FACTS (Flexible AC Transmission) devices connected as shunt compensator in transmission line. The parameters are \(V = 220\) V, frequency \(f = 50\) Hz, reactance \(X = 1.0\ \Omega\), power \(P = 48.4\) kW. What is the value of phase angle \(\alpha\)?

Exam Year(s)

DSSSB AE - 2023,

Answer: A

The key gives \(60^\circ\). For a thyristor controlled reactor the fundamental susceptance depends on the firing angle \(\alpha\) through


\[ \begin{aligned} B(\alpha) \\ &= \frac{1}{X}\left(\frac{2(\pi - \alpha) + \sin 2\alpha}{\pi}\right) \end{aligned} \]


The full reactor at 220 V and 1 ohm would absorb \(220^2/1 = 48.4\) kVA, and the stated power of 48.4 kW is that full value, which corresponds to full conduction. The conduction angle in the item is given in a different convention from the one used here, so I could not reproduce the \(60^\circ\) independently. The explanation follows the key, option A.

Please log in or register to report this question.

5.

The UPFC FACT (Flexible AC Transmission) device can supply ______.

Exam Year(s)

DSSSB AE - 2023,

Answer: C

The unified power flow controller (UPFC) combines a shunt converter (a STATCOM) and a series converter (an SSSC) joined by a common DC link. The series converter can inject a voltage in series with the line, controlling both active and reactive power flow, and the shunt converter can supply or absorb reactive power and provide the real power for the DC link. So a UPFC can supply both active and reactive power, and it also controls the voltage. The answer is option C.

Please log in or register to report this question.

6.

The shunt controller FACT (Flexible AC Transmission) device is:

Exam Year(s)

DSSSB AE - 2023,

Answer: A

A shunt controller of the FACTS family (such as a STATCOM or a static VAR compensator) is connected in parallel with the line and injects current into it at the point of connection, so it acts like a controllable current source. A series controller, in contrast, injects a voltage in series with the line and so acts like a voltage source. The power source and phase angle source options do not describe the way the shunt device acts on the network. The answer is option A.

Please log in or register to report this question.

7.

Which FACT (Flexible AC Transmission) device is the best choice to increase the power transfer capability, for the same level of compensation?

Exam Year(s)

DSSSB AE - 2023,

Answer: B

The power transferred through a line is \(P = \dfrac{V_1V_2}{X}\sin\delta\), and for the same level of compensation a series compensator, a capacitor in series with the line, reduces the effective reactance \(X\) directly and so raises the power limit most effectively. A shunt compensator mainly keeps the mid point voltage near its rated value, which also helps but gives less increase for the same size, and a phase angle regulator changes the angle \(\delta\) rather than the reactance. A voltage source inverter is a building block, not a compensator type. The answer is the series compensator, option B.

Please log in or register to report this question.

8.

The effect of line capacitance in which receiving end voltage is more than the sending end voltage at no load is known as:

Exam Year(s)

DSSSB AE - 2023,

Answer: C

On a long, lightly loaded or open ended transmission line the charging current of the line capacitance flows through the line inductance and raises the voltage along the line, so that the receiving end voltage is greater than the sending end voltage at no load. This is called the Ferranti effect. The thermal effect is the heating of conductors by current, the induction effect is the induced voltage on neighbouring circuits, and humidity effect is not a line effect. The answer is option C.

Please log in or register to report this question.

9.

In the given figure, a three-phase static capacitive reactor of reactance 1 pu per phase is connected through a switch at motor bus bar. Calculate the limit of steady state power with and without reactor switch closed. The internal voltage of the generator is 1.2 pu and that of the motor is 1 pu.

Single line diagram: generator (Xdg = 1.0 pu) with a transformer Xt = 0.1 pu, a line Xt = 0.25 pu, a second transformer Xt = 0.1 pu and a motor (Xdm = 1 pu); a switched capacitive reactor Xc is shunted to ground at the motor bus

Exam Year(s)

DSSSB AE - 2023,

Answer: A

The steady state power limit between two sources is \(P_{max} = \dfrac{E_gE_m}{X_{total}}\). Without the reactor the total reactance is the sum of the series parts.


\[ X = 1.0 + 0.1 + 0.25 + 0.1 + 1.0 = 2.45\ \text{pu} \]


\[ P_{max} = \frac{1.2 \times 1}{2.45} = 0.49\ \text{pu} \]


This is option A, and it is the value without the reactor switch closed. The item asks for the limit with and without the reactor, but the options give a single number, so the key is read as the without reactor figure. With the shunt capacitor switched in at the motor bus, the transfer reactance changes and the limit rises above this value.

Please log in or register to report this question.

Answer: C

The Ferranti effect is the rise in voltage at the receiving end of a long, lightly loaded or open-circuited transmission line, so that the receiving end voltage is greater than the sending end voltage. It is caused by the charging current flowing through the inductance of the line.

The effect does not make either voltage zero, and the sending end voltage is not the greater of the two, since the receiving end is the one that rises. So the third option is correct.

Please log in or register to report this question.

Loading…
Tags: Performance of Transmission Lines Questions and Answers || Performance of Transmission Lines MCQ Questions and Answers || Performance of Transmission Lines GK Questions and Answers || Performance of Transmission Lines GK MCQ Questions || Performance of Transmission Lines Multiple Choice Questions and Answers || Performance of Transmission Lines GK || GK on Performance of Transmission Lines || Power Systems Questions and Answers || Power Systems MCQ Questions and Answers || Power Systems GK Questions and Answers || GK on Power Systems