Instrument Transformers Questions and Answers

41.

A metering current transformer of instrument security factor 5 is rated 100/5. On a fault of 4000 A the secondary current will be at most about

Answer: A

The security factor limits the secondary to five times its rated value, so 25 A, because the core saturates well before the fault current is reached. Without that saturation the instruments would see two hundred amperes and be destroyed.

Please log in or register to report this question.

42.

A protection current transformer rated 500/1 has an accuracy limit factor of 20. It reproduces the primary current faithfully up to

Answer: B

Twenty times the rated primary current is ten kiloamperes, at which the secondary carries twenty amperes. Beyond that the core saturates and the relay would see less than the true fault current, which is why the factor must exceed the largest fault the scheme must clear.

Please log in or register to report this question.

43.

The burden of a current transformer is quoted as 15 VA at 5 A. Its impedance is

Answer: C

Correct answer: 0.6 \( \Omega \)

Burden in volt-amperes converts to impedance through the rated secondary current: \[ Z = \frac{VA}{I^{2}} = \frac{15}{5^{2}} = \frac{15}{25} = 0.6\ \Omega. \] Dividing by the current rather than its square gives the 3 ohms offered, and the square is what makes the next two items behave as they do.

Please log in or register to report this question.

44.

Two instruments of 5 VA and 10 VA at 5 A are connected in series on one current transformer, together with leads of 0.1 \( \Omega \). The total burden is

Answer: D

Correct answer: 17.5 VA

The instruments add directly, and the leads must be converted from ohms at the rated current: \[ 5 + 10 + (0.1 \times 5^{2}) = 5 + 10 + 2.5 = 17.5\ \mathrm{VA}. \] The 15.1 offered adds the lead resistance as though ohms were volt-amperes, and the 15 ignores the leads altogether - which is exactly the mistake that overburdens a current transformer in the field.

Please log in or register to report this question.

45.

Those same 0.1 \( \Omega \) leads on a one ampere secondary would contribute a burden of

Answer: A

Correct answer: 0.1 VA

\[ 0.1 \times 1^{2} = 0.1\ \mathrm{VA}, \] against 2.5 VA for the same leads on a 5 A secondary. The burden goes as the square of the current, so a 1 A secondary imposes a twenty-fifth of the lead burden of a 5 A one. That is the whole reason 1 A current transformers are specified where the cable run between switchgear and panel is long.

Please log in or register to report this question.

46.

A current transformer has a phase angle error of 30 minutes and is used with a wattmeter on a load of 0.5 power factor lagging. The error in the power reading is about

Answer: B

Thirty minutes is 0.00873 radian, and the fractional error is that multiplied by the tangent of sixty degrees, giving \( 0.00873 \times 1.732 = 0.0151 \). The error grows as the power factor falls, which is why phase angle is specified for metering transformers.

Please log in or register to report this question.

47.

A current transformer of nominal ratio 300/5 is found to give 4.98 A when the primary carries 300 A. Its ratio correction factor is about

Answer: C

Correct answer: 1.004

The actual ratio is \( 300/4.98 = 60.24 \) against a nominal 60, and the ratio correction factor is the multiplier that turns the nominal into the true value: \[ \mathrm{RCF} = \frac{60.24}{60} = 1.004. \] Being slightly above unity means the transformer reads low, so the measured current must be scaled up - and a correction of 0.4 per cent is within the tolerance of a metering class transformer.

Please log in or register to report this question.

Answer: D

A current transformer is fed from a current source, so a short is its natural condition and an open circuit drives the core into saturation. A potential transformer is fed from a voltage source, so an open secondary is harmless and a short destroys the winding.

Please log in or register to report this question.

Answer: A

A larger burden means a larger secondary voltage, which means a larger core flux and a larger exciting current, and the exciting current is precisely what constitutes the error. A class is therefore always quoted together with a burden.

Please log in or register to report this question.

Answer: B

Transformer action requires a changing flux to induce a secondary voltage, so a steady current produces nothing in the secondary. Direct current is measured instead by a shunt, a Hall effect device or a saturable reactor arrangement.

Please log in or register to report this question.

Loading…

Other Subjects

Tags: Instrument Transformers Questions and Answers || Instrument Transformers MCQ Questions and Answers || Instrument Transformers GK Questions and Answers || Instrument Transformers GK MCQ Questions || Instrument Transformers Multiple Choice Questions and Answers || Instrument Transformers GK || GK on Instrument Transformers || Electrical Measurements Questions and Answers || Electrical Measurements MCQ Questions and Answers || Electrical Measurements GK Questions and Answers || GK on Electrical Measurements