Demand Side Management Questions and Answers

Answer: C

Correct answer: takes the measure because of the programme without claiming the incentive

A free driver is the opposite case: the programme changed their behaviour but the saving is not recorded against it, usually because they were persuaded by neighbours or by the publicity rather than by applying. Free drivers therefore understate the programme’s effect just as free riders overstate it.

Please log in or register to report this question.

Answer: D

A household given efficient lighting may leave more lights on, and one given efficient heating may heat to a higher temperature, so the realised saving falls short of the engineering estimate. It is a genuine welfare gain and an accounting nuisance.

Please log in or register to report this question.

Answer: A

Correct answer: the surge of demand when a controlled load is restored

When thousands of water heaters or air conditioners are switched back on together, they all draw current at once and the diversity that normally exists between them is gone. The restored peak can exceed the original one, so restoration is staggered in groups rather than done in a single step.

Please log in or register to report this question.

34.

A system with a peak demand of 800 MW and an average demand of 480 MW has a load factor of

Answer: B

Correct answer: 0.60

\[ \frac{480}{800} = 0.60. \] Sixty per cent is typical of a mixed distribution system. A higher figure means the network and the generation are being used more of the time, which is the object of nearly every measure discussed here.

Please log in or register to report this question.

35.

Clipping 80 MW from that 800 MW peak, with the average unchanged, raises the load factor to about

Answer: C

Correct answer: 0.67

The peak falls to 720 MW while the average is unchanged: \[ \frac{480}{720} = 0.667. \] Clipping ten per cent from the peak has raised the load factor by seven points, and it has done so by reducing the denominator - which is why peak reduction is worth more per megawatt hour than a general reduction in consumption.

Please log in or register to report this question.

36.

Ten consumers each with a maximum demand of 50 kW impose a group maximum of 400 kW. The diversity factor is

Answer: D

Correct answer: 1.25

\[ \frac{10 \times 50}{400} = \frac{500}{400} = 1.25. \] The group’s maximum is a fifth less than the sum of its members’ maxima, because they do not all peak together. The factor exceeds one by definition, so an answer below one would indicate the ratio taken the wrong way up.

Please log in or register to report this question.

37.

For that same group, the coincidence factor is

Answer: A

Correct answer: 0.80

\[ \frac{1}{1.25} = 0.80, \] equivalently \( 400/500 \). Eighty per cent of the connected maximum actually coincides. The two factors are reciprocals, so one exceeds unity and the other falls below it - which is the quickest check on whether the right one has been quoted.

Please log in or register to report this question.

38.

A utility avoids 100 MW of peaking capacity costing 40 million per MW. The capital deferred is

Answer: B

Correct answer: 4000 million

\[ 100 \times 40 = 4{,}000\ \mathrm{million}. \] The figure is a deferral rather than a saving outright, since the plant may still be needed later, but deferring capital for several years is worth a substantial fraction of its cost - and it is the avoided capacity, not the avoided energy, that usually justifies a demand side programme.

Please log in or register to report this question.

39.

A programme claims 50 MW of reduction, of which surveys suggest 20 per cent would have occurred anyway. The net reduction is

Answer: C

Correct answer: 40 MW

\[ 50 \times (1 - 0.20) = 40\ \mathrm{MW}. \] The gross figure counts everything the participants did; the net counts only what the programme caused. Since the programme is judged on cost per megawatt actually saved, the free rider adjustment can change a favourable evaluation into an unfavourable one.

Please log in or register to report this question.

Answer: D

Shifting moves consumption in time and removes none of it, which is why it helps the utility's capacity position without hurting its revenue. In practice the off-peak losses are lower, so the generation required falls slightly.

Please log in or register to report this question.

Loading…
Tags: Demand Side Management Questions and Answers || Demand Side Management MCQ Questions and Answers || Demand Side Management GK Questions and Answers || Demand Side Management GK MCQ Questions || Demand Side Management Multiple Choice Questions and Answers || Demand Side Management GK || GK on Demand Side Management || Energy Conservation and Management Questions and Answers || Energy Conservation and Management MCQ Questions and Answers || Energy Conservation and Management GK Questions and Answers || GK on Energy Conservation and Management