Vapour Compression Refrigeration Questions and Answers

Direction for [ Question No: 1 To 2 ] :

Common Data for the next two questions:

A refrigerator operates between 120 kPa and 800 kPa in an ideal vapor compression cycle with R-134a as the refrigerant. The refrigerant enters the compressor as saturated vapor and leaves the condenser as saturated liquid. The mass flow rate of the refrigerant is 0.2 kg/s. Properties for R-134a are as follows:

Saturated R-134a

P (kPa)T (°C)hf (kJ/kg)hg (kJ/kg)sf (kJ/kg.K)sg (kJ/kg.K)
120-22.3222.52370.0930.95
80031.3195.5267.30.3540.918

Superheated R-134a

P (kPa)T (°C)h (kJ/kg)s (kJ/kg.K)
80040276.450.95

1.

The rate at which heat is extracted, in kJ/s from the refrigerated space is

Exam Year(s)

GATE ME - 2012,

Answer: A

Heat is extracted at about 28.3 kJ/s.

In the ideal cycle the refrigerant enters the evaporator at the enthalpy of saturated liquid at 800 kPa (the throttle keeps enthalpy constant) and leaves as saturated vapour at 120 kPa:

\[ \begin{aligned} h_{1} &= h_{g,120} = 237\ \text{kJ/kg} \\ h_{4} &= h_{f,800} = 95.5\ \text{kJ/kg} \\ Q_{L} &= 0.2(237-95.5) = 28.3\ \text{kJ/s} \end{aligned} \]

Using hf at 120 kPa (22.5) instead of at 800 kPa gives 42.9 kJ/s, which ignores the throttling. 34.4 and 14.6 do not follow from the table.

Please log in or register to report this question.

2.

The power required for the compressor in kW is

Exam Year(s)

GATE ME - 2012,

Answer: C

The compressor needs about 7.9 kW.

Compression is isentropic, so the exit entropy equals the inlet entropy sg at 120 kPa, 0.95 kJ/kg.K. At 800 kPa this matches the superheated entry, where h = 276.45 kJ/kg:

\[ \begin{aligned} W &= \dot{m}(h_{2}-h_{1}) \\ &= 0.2(276.45-237) = 7.89\ \text{kW} \end{aligned} \]

Taking the exit as saturated vapour at 800 kPa (267.3) gives 6.1 kW, which is not offered and ignores the superheat. 39.5 forgets the mass flow rate of 0.2 kg/s (39.45 kJ/kg is the specific work), and 1.83 and 5.94 do not follow from the table.

Please log in or register to report this question.

Direction for [ Question No: 3 To 4 ] :

Statement for Linked Answer Questions:

A 1 hp motor is used for running a dual cylinder reciprocating compressor of a refrigeration system based on R-134a refrigerant having 185 kJ kg−1 cooling capacity. COP of the system is 4.2 and overall efficiency of the compressor is 80%. Specific volume of the refrigerant vapour at suction temperature is 0.15 m3 kg−1. The compressor with bore diameters of 40 mm each runs at 1440 rpm.

3.

The mass flow rate of the refrigerant in kg min−1 is

Exam Year(s)

GATE AG - 2012,

Answer: C

The refrigerant mass flow is about 0.813 kg min−1.

The 1 hp motor supplies 0.746 kW. With the compressor 80% efficient, the work delivered to the refrigerant is 0.597 kW, and the COP gives the refrigerating effect:

\[ \begin{aligned} W &= 0.746 \times 0.80 = 0.597\ \text{kW} \\ Q_{e} &= 4.2 \times 0.597 = 2.507\ \text{kW} \\ \dot{m} &= \frac{2.507}{185} = 0.01355\ \text{kg/s} \\ &= 0.813\ \text{kg/min} \end{aligned} \]

Ignoring the compressor efficiency gives about 1.02 kg/min, which is not offered; 1.634 and 1.090 overstate the flow, and 0.240 understates it.

Please log in or register to report this question.

4.

The compressor stroke length in mm is

Exam Year(s)

GATE AG - 2012,

Answer: B

The stroke is about 33.7 mm.

The suction volume flow is \(0.813 \times 0.15 = 0.122\) m3/min. At 1440 rpm, with two single acting cylinders each making one suction stroke per revolution:

\[ \begin{aligned} V_{cyl} &= \frac{0.122}{1440 \times 2} = 4.23 \times 10^{-5}\ \text{m}^{3} \\ A &= \tfrac{\pi}{4}(0.04)^{2} = 1.257 \times 10^{-3}\ \text{m}^{2} \\ L &= V_{cyl}/A = 0.0337\ \text{m} \end{aligned} \]

That is 33.7 mm, taking the volumetric efficiency as 100%. Putting the whole flow through one cylinder doubles the stroke to 67.4 mm, and halving it to 16.8 mm would treat the cylinders as double acting.

Please log in or register to report this question.

Answer: D

The cycle with wet vapour before compression is not a type of vapour compression cycle in the key. In the vapour compression cycle the vapour is compressed in the compressor, and it enters either dry saturated or superheated, and may leave dry saturated or superheated. Compression of wet vapour is avoided because liquid droplets damage the compressor, so it is not a standard cycle, and the other three options are standard types.

Slugging, the entry of liquid into the cylinder, is the damage that wet compression risks, so practical machines are designed to take only dry or superheated vapour.

Please log in or register to report this question.

6.

The condition of refrigerant at the exit of the compressor in a vapor compression refrigeration system is:

Exam Year(s)

GATE AG - 2025,

Answer: D

The refrigerant leaves the compressor as superheated vapor.

In the standard vapor compression cycle, the refrigerant enters the compressor as dry saturated (or slightly superheated) vapor from the evaporator. Compression raises its pressure and, being close to isentropic, raises its temperature above the saturation temperature at the condenser pressure, so it leaves superheated.

Saturated liquid is the state at the condenser exit, before the expansion valve. Wet vapor is the state after the expansion valve, entering the evaporator. Dry saturated vapor is the usual state at the compressor inlet, not the outlet.

Please log in or register to report this question.

7.

In a vapour compression refrigeration cycle, the refrigerant enters the compressor in saturated vapour state at evaporator pressure, with specific enthalpy equal to 250 kJ/kg. The exit of the compressor is superheated at condenser pressure with specific enthalpy equal to 300 kJ/kg. At the condenser exit, the refrigerant is throttled to the evaporator pressure. The coefficient of performance (COP) of the cycle is 3. If the specific enthalpy of the saturated liquid at evaporator pressure is 50 kJ/kg, then the dryness fraction of the refrigerant at entry to evaporator is _________.

Exam Year(s)

GATE ME - 2022,

Answer: B

The dryness fraction at entry to the evaporator is 0.25.

Number the states: 1 evaporator exit (saturated vapour, \(h_{1} = 250\) kJ/kg), 2 compressor exit (\(h_{2} = 300\) kJ/kg), 3 condenser exit, 4 after throttling. Throttling keeps enthalpy constant, so \(h_{4} = h_{3}\).

\[ \begin{aligned} COP &= \frac{h_{1} - h_{4}}{h_{2} - h_{1}} = \frac{250 - h_{4}}{50} = 3 \\ h_{4} &= 250 - 150 = 100\ \text{kJ/kg} \end{aligned} \]

State 4 is a wet mixture at evaporator pressure, between saturated liquid (\(h_{f} = 50\)) and saturated vapour (\(h_{g} = 250\)):

\[ \begin{aligned} x_{4} &= \frac{h_{4} - h_{f}}{h_{g} - h_{f}} \\ &= \frac{100 - 50}{250 - 50} = 0.25 \end{aligned} \]

0.2 divides by 250 instead of by the latent enthalpy 200 (50/250). 0.3 and 0.35 do not follow from the given enthalpies; any error in the COP step changes \(h_{4}\) and every later figure.

Please log in or register to report this question.

Loading…
Tags: Vapour Compression Refrigeration Questions and Answers || Vapour Compression Refrigeration MCQ Questions and Answers || Vapour Compression Refrigeration GK Questions and Answers || Vapour Compression Refrigeration GK MCQ Questions || Vapour Compression Refrigeration Multiple Choice Questions and Answers || Vapour Compression Refrigeration GK || GK on Vapour Compression Refrigeration || Refrigeration and Air Conditioning Questions and Answers || Refrigeration and Air Conditioning MCQ Questions and Answers || Refrigeration and Air Conditioning GK Questions and Answers || GK on Refrigeration and Air Conditioning