Machine-translated by Google. Questions are authored in English.
Top

Refrigeration and Air Conditioning Questions and Answers

1.

Determine the C.O.P. of a refrigeration system if the work input is 80 kJ/kg and refrigeration effect produced is 120 kJ/kg of refrigerant flowing?

Exam Year(s)

DSSSB - 2023,

Answer: B

The COP is 1.5. The coefficient of performance of a refrigerator is the refrigeration effect divided by the work input: \[ COP = \frac{120}{80} = 1.5 \] The value 1.33 would result from dividing 80 by 60 and 2.0 and 3.0 do not follow from dividing 120 by 80, so only 1.5 is right.

Please log in or register to report this question.

2.

Which is one of the non-conventional refrigeration methods used for producing low temperature on the basis of the reverse seebeck effect?

Exam Year(s)

DSSSB - 2023,

Answer: B

Thermoelectric refrigeration produces low temperature by the reverse of the Seebeck effect, which is the Peltier effect: a current passed through a junction of two dissimilar conductors absorbs heat at one junction. Magnetic refrigeration works on the magnetocaloric effect, liquid gas refrigeration on the evaporation of a liquefied gas, and dry ice refrigeration on the sublimation of solid carbon dioxide, so only the thermoelectric method matches the effect named.

Please log in or register to report this question.

3.

A refrigeration system based on reverse Carnot cycle operates between −30 °C and 20 °C. The refrigeration capacity of the system is 70 kW. Heat rejected at the condenser to atmosphere (hot reservoir), in kW, is nearest to

Exam Year(s)

GATE AG - 2026,

Answer: A

The heat rejected is about 84.40 kW.

A reversed Carnot cycle must use absolute temperatures: \(T_{L} = 243\) K and \(T_{H} = 293\) K.

\[ \begin{aligned} COP &= \frac{T_{L}}{T_{H} - T_{L}} = \frac{243}{50} = 4.86 \\ W &= \frac{70}{4.86} = 14.40\ \text{kW} \\ Q_{H} &= Q_{L} + W = 84.40\ \text{kW} \end{aligned} \]

14.41 kW is the compressor work, not the heat rejected. 116.67 kW is what the work comes to if the temperatures are left in degrees Celsius (COP = 30/50 = 0.6), and 186.67 kW is 70 plus that wrong work. Heat rejected must always be the refrigeration load plus the work input.

Please log in or register to report this question.

4.

The COP of a heat pump operating between 6°C and 37°C will be:

Exam Year(s)

RSMSSB JE - 2025, RSMSSB - 2025,

Answer: B

The COP is 10.

For a reversible heat pump, with temperatures in kelvin, \(T_{H} = 37 + 273 = 310\) K and \(T_{L} = 6 + 273 = 279\) K:

\[ \begin{aligned} COP_{HP} &= \frac{T_{H}}{T_{H} - T_{L}} \\ &= \frac{310}{31} = 10 \end{aligned} \]

Using the refrigerator formula \(T_{L}/(T_{H} - T_{L}) = 279/31 = 9\) gives one less, because \(COP_{HP} = COP_{R} + 1\). Using degrees Celsius instead of kelvin gives nonsense values. 8, 12 and 14 do not come from the correct temperatures.

Please log in or register to report this question.

5.

An industrial heat pump operates between the temperature of 27°C and -13°C. The rates of heat addition and heat rejection are 750W and 1000W, respectively. The COP for the heat pump is:

Exam Year(s)

RSMSSB JE - 2025, RSMSSB - 2025,

Answer: C

The COP of the heat pump is 4.0.

A heat pump's COP is the heat delivered to the hot side divided by the work input. The work is the difference between heat rejected and heat added:

\[ \begin{aligned} W &= 1000 - 750 = 250\ \text{W} \\ COP_{HP} &= \frac{1000}{250} = 4.0 \end{aligned} \]

7.5 is the Carnot COP, \(300/40\), for these temperatures, an upper limit rather than the actual value. 3.0 is \(750/250\), the COP if the machine were judged as a refrigerator. 6.5 does not follow from the data.

Please log in or register to report this question.

6.

A reversed carnot cycle refrigerator maintains a temperature of -5°C.The ambient air temperature is 35°C.The heat gained by the refrigerator at a continuous rate is 2.5 kJ/sec.What will be (COP) of refrigerator?

Exam Year(s)

RSMSSB JE - 2025, RSMSSB - 2025,

Answer: A

The COP is 6.7.

For a reversed Carnot refrigerator, with \(T_{L} = -5 + 273 = 268\) K and \(T_{H} = 35 + 273 = 308\) K:

\[ \begin{aligned} COP &= \frac{T_{L}}{T_{H} - T_{L}} \\ &= \frac{268}{40} = 6.7 \end{aligned} \]

The 2.5 kJ/s heat load is not needed for the COP; it would be used to find the power input, \(2.5/6.7 = 0.37\) kW. The nearby values 6.6, 6.5 and 6.4 come from rounding or from using 273.15 inconsistently.

Please log in or register to report this question.

7.

One ton of refrigeration heat is equivalent to the amount of heat required to melt 1 ton of ice at 0°C in-

Exam Year(s)

RSMSSB JE - 2025, RSMSSB JE Agriculture - 2025, RSMSSB - 2025,

Answer: C

One ton of refrigeration is the heat needed to melt 1 ton of ice at 0°C in 24 hours.

The unit comes from the days when cooling was done with ice. Melting one short ton (2,000 lb) of ice absorbs 2,000 times its latent heat of 144 Btu/lb, spread over a day:

\[ \begin{aligned} \text{TR} &= \frac{2000 \times 144}{24} \\ &= 12{,}000\ \text{Btu/h} \approx 3.517\ \text{kW} \end{aligned} \]

Taking 1 hour instead would make the unit 24 times larger, 12 hours twice as large, and 1 minute 1,440 times as large. The day-long rate is what defines the ton.

Please log in or register to report this question.

Loading…
Tags: Refrigeration Fundamentals Questions and Answers || Refrigeration Fundamentals MCQ Questions and Answers || Refrigeration Fundamentals GK Questions and Answers || Refrigeration Fundamentals GK MCQ Questions || Refrigeration Fundamentals Multiple Choice Questions and Answers || Refrigeration Fundamentals GK || GK on Refrigeration Fundamentals || Refrigeration and Air Conditioning Questions and Answers || Refrigeration and Air Conditioning MCQ Questions and Answers || Refrigeration and Air Conditioning GK Questions and Answers || GK on Refrigeration and Air Conditioning