Psychrometric Processes Questions and Answers

1.

Which point on the psychrometric chart represents the condition of the air coming out of the cooling coil in an air conditioning system?

Exam Year(s)

DSSSB - 2023,

Answer: C

The condition of air coming out of the cooling coil is the apparatus dew point (ADP) on the psychrometric chart, which is the temperature of the coil surface when the air is cooled below its dew point. The wet bulb and dry bulb temperatures are properties of the air, not specific to the cooling coil's outlet, and 'dry point' is not a term used on the chart.

Please log in or register to report this question.

2.

Air at 70 °C and 0.015 humidity ratio is cooled adiabatically by spraying water. The final temperature of the air is 55 °C. Specific heat capacities of dry air and water vapour are 1.005 and 1.88 kJ kg−1 K−1, respectively and latent heat of vapourization of water at 0 °C is 2501.7 kJ kg−1. The absolute humidity of the outlet air, in kg water vapour per kg dry air is

Exam Year(s)

GATE AG - 2012,

Answer: C

The outlet humidity is about 0.021 kg/kg dry air.

Adiabatic cooling by spraying water keeps the enthalpy of the moist air essentially constant, with \(h = 1.005\,t + W(2501.7 + 1.88\,t)\) in kJ per kg dry air:

\[ \begin{aligned} h_{1} &= 1.005(70) + 0.015(2501.7 + 131.6) \\ &= 70.35 + 39.50 = 109.85 \\ 109.85 &= 1.005(55) + W_{2}(2501.7 + 103.4) \\ W_{2} &= \frac{109.85 - 55.28}{2605.1} = 0.0209 \end{aligned} \]

The air gains about 0.006 kg of water per kg dry air as it cools by 15 °C. 0.017 and 0.019 add too little moisture to balance the sensible heat given up, and 0.023 adds too much.

Please log in or register to report this question.

3.

Match the following psychrometric processes (Column I) with the respective changes in thermodynamic properties (Column II) of air-water vapor mixture:

Column IColumn II
1Sensible coolingPDry bulb temperature increases and dew point temperature decreases
2Cooling and dehumidificationQDry bulb temperature increases and dew point temperature increases
3Chemical dehumidificationRDry bulb temperature decreases and dew point temperature remains constant
4Heating and humidificationSDry bulb temperature decreases and dew point temperature decreases

Exam Year(s)

GATE AG - 2025,

Answer: C

The correct matching is 1-R, 2-S, 3-P, 4-Q.

Dew point temperature depends only on the moisture content (humidity ratio) of the air, so it moves with moisture, while the dry bulb temperature follows heating or cooling.

  1. Sensible cooling removes heat at constant moisture, so dry bulb falls and dew point stays constant: R.
  2. Cooling and dehumidification lowers the temperature and condenses moisture out, so both fall: S.
  3. Chemical dehumidification by an adsorbent removes moisture and releases the heat of adsorption, so dew point falls while dry bulb rises: P.
  4. Heating and humidification adds both heat and moisture, so both rise: Q.

The first option swaps the pairings for chemical dehumidification and heating with humidification. The second and fourth options pair sensible cooling with a rising dry bulb temperature, which is impossible for a cooling process.

Please log in or register to report this question.

4.

At 60 °C dry bulb temperature, saturated water vapour pressure is 20 kPa and relative humidity is 20%. The corresponding absolute humidity of air at atmospheric pressure is nearest to

(Take molecular weight of water = 18.02 g.mol−1, molecular weight of air = 28.97 g.mol−1, and atmospheric pressure = 101.325 kPa)

Exam Year(s)

GATE AG - 2026,

Answer: A

The absolute humidity is about 0.026 kg water per kg dry air.

The partial pressure of the vapour is the relative humidity times the saturation pressure, and the humidity ratio follows from the molar mass ratio:

\[ \begin{aligned} p_{v} &= 0.20 \times 20 = 4\ \text{kPa} \\ H &= \frac{18.02}{28.97} \cdot \frac{p_{v}}{P - p_{v}} \\ &= 0.622 \times \frac{4}{101.325 - 4} \\ &= 0.622 \times 0.0411 = 0.0256 \end{aligned} \]

That rounds to 0.026. 0.041 is the pressure ratio \(p_{v}/(P - p_{v})\) without the molar-mass factor 0.622. 0.004 and 0.032 do not come from the correct vapour pressure of 4 kPa; using the saturation pressure of 20 kPa instead would give a much larger 0.153.

Please log in or register to report this question.

Loading…
Tags: Psychrometric Processes Questions and Answers || Psychrometric Processes MCQ Questions and Answers || Psychrometric Processes GK Questions and Answers || Psychrometric Processes GK MCQ Questions || Psychrometric Processes Multiple Choice Questions and Answers || Psychrometric Processes GK || GK on Psychrometric Processes || Refrigeration and Air Conditioning Questions and Answers || Refrigeration and Air Conditioning MCQ Questions and Answers || Refrigeration and Air Conditioning GK Questions and Answers || GK on Refrigeration and Air Conditioning