Overcurrent Protection Questions and Answers

1.

An over current relay, having a current setting of 12.5%, is connected to a supply circuit through a current transformer, with a ratio of 400/8. Find the pickup value of the current.

Exam Year(s)

DSSSB AE - 2023,

Answer: C

The plug setting of an over current relay is a percentage of the rated secondary current of the current transformer. A CT with a ratio of 400/8 has a rated secondary current of 8 A.


\[ \begin{aligned} \text{Pick up current} \\ &= 12.5\% \times 8\ \text{A} = 0.125 \times 8 \\ &= 1\ \text{A} \end{aligned} \]


This is the current in the relay coil at which it picks up; the primary current that causes it is \(1 \times 50 = 50\) A, because the CT ratio is 50. The values 5 A, 2.5 A and 0.5 A do not match 12.5% of 8 A. The answer is 1 A, option C.

Please log in or register to report this question.

2.

Which of the following is NOT a type of power system protective scheme?

Exam Year(s)

DSSSB AE - 2023,

Answer: D

The common protective schemes in a power system are over current protection, distance (impedance) protection, differential protection, carrier-current (pilot) protection and earth fault protection. Each responds to an electrical quantity such as current, impedance or a signal sent over the line. Humidity is a condition of the air and not an electrical quantity that a relay measures, so humidity protection is not a type of protective scheme. The answer is option D.

Please log in or register to report this question.

3.

In power system, for extremely inverse over current protection scheme, the fault current is 25 A. Calculate the time in which the fault will be cleared if the time multiplier setting is 100%?

Exam Year(s)

DSSSB AE - 2023,

Answer: A

The key gives 0.128 s. For an extremely inverse over current relay the operating time is inversely proportional to the square of the plug setting multiplier, \(t = \dfrac{80\,\text{TMS}}{PSM^2 - 1}\) in the standard IEC form. With the fault current of 25 A and the time multiplier setting of 100 per cent, the plug setting multiplier depends on a relay setting that the item does not print, so the stated data do not let the value be derived independently. The explanation follows the key, option A, and the answer is of the order of a fraction of a second, which is typical for an extremely inverse curve at a high multiple of the setting.

Please log in or register to report this question.

4.

In power system protection, the term "relay co-ordination" refers to :

Exam Year(s)

RSMSSB JE - 2025, RSMSSB - 2025,

Answer: A

Relay co-ordination refers to the timing of protection relays.

In a network, several relays see the same fault current. Co-ordination sets their current and time settings so that the relay nearest the fault trips first and isolates the smallest part of the system, while relays further back wait a grading interval, typically 0.3 to 0.5 s, and act only as back-up if it fails.

It has nothing to do with balancing load or placing current transformers. Mal-operation of relays is what good co-ordination prevents, not what the term means.

Please log in or register to report this question.

Loading…
Tags: Overcurrent Protection Questions and Answers || Overcurrent Protection MCQ Questions and Answers || Overcurrent Protection GK Questions and Answers || Overcurrent Protection GK MCQ Questions || Overcurrent Protection Multiple Choice Questions and Answers || Overcurrent Protection GK || GK on Overcurrent Protection || Switchgear and Protection Questions and Answers || Switchgear and Protection MCQ Questions and Answers || Switchgear and Protection GK Questions and Answers || GK on Switchgear and Protection