11.

The lag adjustment of a meter is checked at a power factor of

Answer: C

An error in the quadrature angle shows itself as a power factor dependent error, so it is invisible at unity power factor and plain at 0.5. The routine is to set the full-load speed at unity power factor with the braking magnet, then correct the lag at 0.5.

Please log in or register to report this question.

Answer: D

Moving the magnet outward increases the radius at which the eddy currents act and so the braking torque, which slows the disc and reduces the registration. This is the coarse speed adjustment and it is made at rated current and unity power factor.

Please log in or register to report this question.

Answer: A

Friction is roughly constant while the driving torque falls with the load, so at five per cent of rated current it may be an appreciable fraction of the torque and the meter would run slow. A small extra torque, obtained from a shading loop near the shunt magnet, makes up for it.

Please log in or register to report this question.

Answer: B

A copper loop or vane placed asymmetrically under the shunt magnet pole splits its flux into two components slightly out of phase, and those two produce a small torque proportional to the square of the voltage. That torque is present whatever the load and offsets the friction.

Please log in or register to report this question.

Answer: C

It is the classic consequence of over-generous friction compensation, though vibration, stray fields and an excessive supply voltage can also produce it. The meter then registers energy that has not been consumed, which is why it must be prevented.

Please log in or register to report this question.

Answer: D

As a hole approaches the shunt magnet pole the eddy current pattern is distorted and a torque arises that holds the disc there. Any creeping motion therefore stops within half a revolution, while at normal speeds the effect is negligible.

Please log in or register to report this question.

Answer: A

Saturation makes the series flux rise less than in proportion to the current, so the meter would register low on overload. A magnetic shunt across the series magnet, or a saturable flux diverter, restores the proportionality over the working range.

Please log in or register to report this question.

18.

Which adjustment of an energy meter is made at rated current and unity power factor?

Answer: B

The full-load speed is set first with the braking magnet at rated current and unity power factor, because everything else is a correction to it. The lag adjustment follows at 0.5 power factor and the friction adjustment at about five per cent of rated current.

Please log in or register to report this question.

Answer: C

It is marked on the nameplate as a figure such as 1200 rev/kWh, and dividing the revolutions counted by that figure gives the energy. The reciprocal is sometimes quoted as the disc constant in watt hours per revolution, but the usual marking is the first form.

Please log in or register to report this question.

Answer: D

The pressure circuit is fed at rated voltage from one source while the current circuit is fed at rated current from a separate low-voltage source. The power drawn is then only the losses of the two circuits, which for a large meter is a great saving.

Please log in or register to report this question.

Loading…

Other Subjects

Tags: Energy Meters Questions and Answers || Energy Meters MCQ Questions and Answers || Energy Meters GK Questions and Answers || Energy Meters GK MCQ Questions || Energy Meters Multiple Choice Questions and Answers || Energy Meters GK || GK on Energy Meters || Electrical Measurements Questions and Answers || Electrical Measurements MCQ Questions and Answers || Electrical Measurements GK Questions and Answers || GK on Electrical Measurements