Instrument Transformers Questions and Answers

Answer: C

Ideally the reversed secondary current would be exactly in phase with the primary. The exciting current tilts it by a small angle, usually a few minutes, and that angle matters in any measurement involving phase, such as power, energy or a directional relay.

Please log in or register to report this question.

Answer: D

An ammeter responds to magnitude alone and is untroubled by a few minutes of phase shift. A wattmeter multiplies by a cosine, so a small angle error becomes a power error, and it becomes a large one when the load power factor is low.

Please log in or register to report this question.

Answer: A

Reducing the secondary turns by one or two raises the secondary current a little, which offsets the part of the primary current lost to magnetisation. It corrects the ratio error at one chosen current and burden but does nothing for the phase angle error.

Please log in or register to report this question.

Answer: B

Removing a turn scales the secondary current but does not rotate it, so the angle between primary and reversed secondary current is unaffected. The phase angle is reduced instead by improving the core material and lowering the burden.

Please log in or register to report this question.

Answer: C

The exciting current does not fall in proportion to the primary current, so at a tenth of rated current it is a much larger fraction of the whole and the error is correspondingly worse. Accuracy classes therefore specify limits at several fractions of rated current.

Please log in or register to report this question.

Answer: D

With no secondary current to oppose it the whole primary current becomes exciting current. The core is driven far into saturation, the flux waveform becomes peaky and the induced secondary voltage may reach thousands of volts, endangering both the insulation and the operator.

Please log in or register to report this question.

Answer: A

A shorted secondary is the safe condition for a current transformer, the opposite of the rule for a voltage transformer. Shorting links are provided on the terminal block for exactly this, and the transformer suffers nothing while shorted.

Please log in or register to report this question.

Answer: B

A short circuit is a burden of zero impedance, which gives the smallest possible secondary voltage and hence the smallest core flux and the smallest error. It is the condition of least stress on the transformer in every respect.

Please log in or register to report this question.

Answer: C

A low security factor is wanted for a metering transformer, so that on a fault the core saturates early and the instruments are shielded from the enormous current. A factor of five means the secondary current cannot exceed five times rated however large the fault.

Please log in or register to report this question.

20.

The accuracy limit factor of a protection current transformer is wanted

Answer: D

A protection transformer must reproduce the fault current faithfully, since that is precisely what the relay has to measure. A factor of ten or twenty means the ratio holds up to ten or twenty times rated primary current, which is the opposite requirement to a metering core.

Please log in or register to report this question.

Loading…

Other Subjects

Tags: Instrument Transformers Questions and Answers || Instrument Transformers MCQ Questions and Answers || Instrument Transformers GK Questions and Answers || Instrument Transformers GK MCQ Questions || Instrument Transformers Multiple Choice Questions and Answers || Instrument Transformers GK || GK on Instrument Transformers || Electrical Measurements Questions and Answers || Electrical Measurements MCQ Questions and Answers || Electrical Measurements GK Questions and Answers || GK on Electrical Measurements