Answer: C

The requirement is the opposite: a metering core should saturate early so that fault current is not passed on to delicate instruments. That property is expressed as a low instrument security factor, and it is the protection core that wants a high accuracy limit factor.

Please log in or register to report this question.

Answer: D

With no secondary current the whole primary current becomes exciting current, the core saturates and a peaky induced voltage of thousands of volts may appear. Shorting the terminals removes the hazard, and it is exactly for that reason that the practice exists.

Please log in or register to report this question.

Answer: A

Lead burden is proportional to the square of the secondary current, so a fivefold reduction in current reduces it twenty-five-fold. In a large station where the instruments are far away that is the decisive consideration, and it is the reason given.

Please log in or register to report this question.

Answer: B

The light loading follows from the burden being only a voltmeter or relay coil, not from the core material. Good core material does help the accuracy, but it is not the reason the transformer is lightly loaded, so the two true statements are unconnected.

Please log in or register to report this question.

55.

Match the quantity with the type of transformer it belongs to.

1. Knee point voltage   2. Instrument security factor   3. Tuning inductance

P. Metering current transformer   Q. Capacitive voltage transformer   R. Protection current transformer

Answer: C

The knee point defines where a protection core stops reproducing fault current; the security factor says how early a metering core saturates to shield its instruments; and the tuning inductance makes a capacitor divider behave as a stiff source at power frequency.

Please log in or register to report this question.

56.

Match the fault with what it causes.

1. Open circuited current transformer secondary   2. Short circuited potential transformer secondary   3. Excessive burden on a current transformer

P. Increased ratio and phase angle error   Q. Destruction of the winding   R. Dangerous secondary voltage

Answer: D

Each fault follows from which kind of source feeds the transformer. A current source drives its core to saturation when denied a path; a voltage source pours current into a short; and an excessive but finite burden merely raises the flux and with it the errors.

Please log in or register to report this question.

57.

The steps of removing a wattmeter from a current transformer circuit in service are listed below. Put them in order.

1. Disconnect the instrument leads   2. Close the shorting link across the secondary terminals   3. Remove the instrument   4. Check that the shorting link is making good contact

Answer: A

Correct answer: 2, 4, 1, 3

The shorting link goes on first and is then checked, because an open-circuited current transformer secondary is dangerous: the primary current becomes pure magnetising current, the core saturates hard and very high voltages appear across the open terminals. Only once the short is proved may the instrument leads be disconnected and the instrument removed. This ordering is a safety rule, not a preference.

Please log in or register to report this question.

58.

Consider the following statements about current transformers.

1. The errors are worst at low primary current   2. Turns compensation corrects the ratio error   3. Turns compensation corrects the phase angle error

Answer: B

The exciting current is a larger fraction of a small primary current, so the percentage error is worst there. Removing a secondary turn scales the secondary current and so corrects the ratio, but it cannot rotate it and so leaves the phase angle untouched.

Please log in or register to report this question.

59.

Consider the following statements about potential transformers.

1. The secondary is fused   2. Increasing the burden increases the errors   3. The secondary may be safely short circuited

Answer: C

A fuse is fitted precisely because a short must be cleared quickly, so the third statement is false. The first two are correct: the burden current produces the winding drops that constitute the ratio and phase angle errors.

Please log in or register to report this question.

Answer: D

Correct answer: to improve the accuracy of the instrument beyond its own class

An instrument transformer can only add its own errors of ratio and phase angle to those of the instrument; it cannot make a class 1 instrument better than class 1. The three genuine reasons are all present: isolation from system voltage, the use of standard 5 A and 110 V instruments at any system rating, and a small burden drawn from the circuit measured.

Please log in or register to report this question.

Loading…
Tags: Instrument Transformers Questions and Answers || Instrument Transformers MCQ Questions and Answers || Instrument Transformers GK Questions and Answers || Instrument Transformers GK MCQ Questions || Instrument Transformers Multiple Choice Questions and Answers || Instrument Transformers GK || GK on Instrument Transformers || Electrical Measurements Questions and Answers || Electrical Measurements MCQ Questions and Answers || Electrical Measurements GK Questions and Answers || GK on Electrical Measurements