Transformers Questions and Answers

Answer: A

The neutral is what makes a four-wire distribution system possible and gives a reference for earthing and protection. A delta winding gives the closed path for triple harmonics, which is why the two are often combined.

Please log in or register to report this question.

Answer: B

Triple harmonics circulate within the delta rather than distorting the voltage or flowing in the neutral, which is why a delta winding is usual on at least one side. The winding current is \( 1/\sqrt{3} \) of the line current.

Please log in or register to report this question.

Answer: C

Correct answer: distortion of the phase voltages by triple harmonics

The magnetising current contains a strong third harmonic, and in a star-star connection with no delta winding and no neutral path that harmonic current cannot circulate. It is therefore forced into the flux instead, and the phase voltages are distorted by a large third harmonic. A delta tertiary provides the circulating path and cures it.

Please log in or register to report this question.

Answer: D

Correct answer: give a path for triple harmonic and unbalance currents

A closed delta tertiary lets triple harmonic magnetising currents circulate within it rather than distorting the flux, and it also provides a path for zero sequence current under unbalanced loading, so the neutral is stabilised. It is often used to supply station auxiliaries as well, but that is a convenience rather than its purpose.

Please log in or register to report this question.

Answer: A

Two units can supply a three-phase load at about fifty-eight per cent of the bank's rating, which keeps supply going while the third is repaired. That resilience is one reason the connection was favoured for industrial supplies.

Please log in or register to report this question.

Answer: B

Two specially proportioned transformers give two single-phase outputs in quadrature that load the three-phase system evenly, which suits electric traction. Without such an arrangement a single-phase traction load unbalances the supply badly.

Please log in or register to report this question.

Answer: C

Its geometry gives a low impedance to zero-sequence current and a high one to positive sequence, which makes it an effective earthing transformer on a delta system. It is a special-purpose connection rather than a general one.

Please log in or register to report this question.

Answer: D

A ratio mismatch circulates current between them even at no load, and a polarity or phase sequence error is a short circuit. Equal per unit impedances are desirable for proportional sharing but are not an absolute requirement.

Please log in or register to report this question.

Answer: A

Correct answer: share the load in inverse proportion to those impedances

Paralleled transformers see the same terminal voltage, so the one with the lower impedance takes the larger share of current: the split is in inverse proportion to the per unit impedances. Unequal impedances therefore mean one unit reaches its rating before the other, and the pair cannot deliver the sum of their ratings.

Please log in or register to report this question.

Answer: B

A thirty degree difference in secondary phase leaves a large voltage between the paralleled terminals, and only the winding impedances limit the resulting current. It is a fault condition rather than a poor arrangement.

Please log in or register to report this question.

Loading…
Tags: Transformers Questions and Answers || Transformers MCQ Questions and Answers || Transformers GK Questions and Answers || Transformers GK MCQ Questions || Transformers Multiple Choice Questions and Answers || Transformers GK || GK on Transformers || Electrical Machines Questions and Answers || Electrical Machines MCQ Questions and Answers || Electrical Machines GK Questions and Answers || GK on Electrical Machines