Machine-translated by Google. Questions are authored in English.
Top

Transformers Questions and Answers

Direction for [ Question No: 1 To 2 ] :

A transformer with 800 primary turns and 200 secondary turns is supplied from a 100 V A.C. supply.

1.

Calculate the Secondary Voltage:

Exam Year(s)

Northern Coalfields Limited - 2020, NCL Technician - 2020,

Answer: B

The secondary voltage is 25 V.

In a transformer the voltage per turn is the same on both windings, so the voltages are in the ratio of the turns:

\[ \begin{aligned} \frac{V_{2}}{V_{1}} &= \frac{N_{2}}{N_{1}} \\ V_{2} &= 100 \times \frac{200}{800} = 25\ \text{V} \end{aligned} \]

With fewer secondary turns this is a step-down transformer. 400 V inverts the ratio (\(100 \times 800/200\)), treating it as step-up; 250 V and 40 V do not follow from the turns ratio at all.

Please log in or register to report this question.

2.

Calculate the Volts per turn:

Exam Year(s)

Northern Coalfields Limited - 2020, NCL Technician - 2020,

Answer: D

The volts per turn is 0.125.

Volts per turn is the applied voltage divided by the turns on that winding:

\[ \begin{aligned} \frac{V_{1}}{N_{1}} &= \frac{100}{800} \\ &= 0.125\ \text{V per turn} \end{aligned} \]

The secondary gives the same figure, \(25/200 = 0.125\), as it must, since both windings link the same flux.

8 is turns per volt (\(800/100\)) rather than volts per turn, 4 is the turns ratio \(800/200\), and 0.25 is double the correct figure.

Please log in or register to report this question.

3.

The emf induced in a transformer winding is given by

Answer: A

Correct answer: \( 4.44fN\Phi_m \)

The induced emf is the rate of change of flux linkage, and for sinusoidal flux the rms value works out as \[ E = 4.44\,f\,N\,\Phi_m, \] where 4.44 is \( 2\pi/\sqrt{2} \). Everything follows from it: the flux is fixed by the applied voltage and frequency, which is why core loss is nearly constant with load, and why a transformer run at reduced frequency saturates.

Please log in or register to report this question.

Answer: B

Induction requires a changing flux linkage, and direct current gives a steady flux once the transient has died away. The primary then behaves as a low resistance across the supply, which is why applying dc to a transformer destroys it.

Please log in or register to report this question.

Answer: C

Correct answer: the turns ratio of its windings

Both windings link the same core flux, so each develops \( 4.44fN\Phi_m \) and the ratio of the two voltages is simply the ratio of the turns. That is exactly why the flux term cancels and the relation holds regardless of frequency, core material or size - it is the defining property of the transformer.

Please log in or register to report this question.

Answer: D

Correct answer: the inverse of the turns ratio

Neglecting the small magnetising current, the ampere-turns of the two windings must balance, so \( N_1I_1 = N_2I_2 \) and the current ratio is the inverse of the turns ratio. The winding with more turns carries less current, which is why the high-voltage winding is wound in finer wire and why tap changers are placed there.

Please log in or register to report this question.

7.

An impedance referred from the secondary to the primary of a transformer is multiplied by

Answer: A

Correct answer: the square of the turns ratio

Voltage transforms by the turns ratio and current by its inverse, so impedance, being their quotient, transforms by the square: \( Z_1 = (N_1/N_2)^2 Z_2 \). This is the basis of impedance matching, and it is why per unit quantities are so convenient - expressed in per unit, an impedance has the same value on either side.

Please log in or register to report this question.

8.

A transformer with 1,000 primary and 250 secondary turns fed at 400 V gives a secondary voltage of

Answer: B

Correct answer: 100 V

\[ V_2 = V_1\frac{N_2}{N_1} = 400 \times \frac{250}{1000} = 100\ \text{V.} \] The transformer steps down by four to one, so the secondary voltage is a quarter of the primary. The distractor of 1600 V is what you get by inverting the ratio, which is the usual slip when the direction of transformation is not fixed in mind first.

Please log in or register to report this question.

9.

That transformer supplying 20 A on its secondary draws a primary current of about

Answer: C

Correct answer: 5 A

Ampere-turns balance, so the current transforms by the inverse of the turns ratio: \[ I_1 = I_2\frac{N_2}{N_1} = 20 \times \frac{250}{1000} = 5\ \text{A.} \] Check it against the power: the secondary delivers \( 100 \times 20 = 2000 \) VA and the primary draws \( 400 \times 5 = 2000 \) VA, as it must if losses are neglected.

Please log in or register to report this question.

10.

A load impedance of 4 Ω on the secondary of that transformer appears at the primary as

Answer: D

Correct answer: 64 Ω

Impedance transforms by the square of the turns ratio: \[ Z_1 = \left(\frac{N_1}{N_2}\right)^2 Z_2 = 4^2 \times 4 = 64\ \Omega. \] Forgetting the square gives 16, which is one of the distractors. A step-down transformer therefore makes a low impedance look large from the primary side, which is precisely what impedance matching exploits.

Please log in or register to report this question.

Loading…
Tags: Transformers Questions and Answers || Transformers MCQ Questions and Answers || Transformers GK Questions and Answers || Transformers GK MCQ Questions || Transformers Multiple Choice Questions and Answers || Transformers GK || GK on Transformers || Electrical Machines Questions and Answers || Electrical Machines MCQ Questions and Answers || Electrical Machines GK Questions and Answers || GK on Electrical Machines