Answer: A

Thin sheets separated by insulation break up the paths available to circulating currents, and the loss falls with the square of the thickness. Hysteresis loss depends on the grade of steel rather than on the lamination.

Please log in or register to report this question.

Answer: B

Aligning the crystal grains with the direction the flux will take reduces the loss and raises the permeability along that axis. Mitred corner joints are used so that the flux stays as nearly as possible in the favourable direction.

Please log in or register to report this question.

Answer: D

Even a few parts per million of water lowers the breakdown voltage sharply, which is why the breather dries the incoming air and the oil is filtered and dried in service. Particles and acidity from ageing also contribute.

Please log in or register to report this question.

Answer: A

Different faults produce characteristic mixtures of hydrogen, methane, acetylene and the rest, so the ratios point to overheating, partial discharge or arcing. It is the principal condition-monitoring tool for a large transformer.

Please log in or register to report this question.

Answer: B

Correct answer: the winding and the top oil, each with its own limit

Two limits are specified because they measure different things: the top oil temperature governs the ageing of the oil, while the winding temperature, always the higher of the two, governs the ageing of the paper insulation. Insulation life falls roughly by half for each 6 to 8 degrees of sustained excess, which is why both are monitored.

Please log in or register to report this question.

Answer: C

The losses are unchanged, but a lower thermal resistance to ambient means the same temperature rise accommodates a larger loss and therefore a larger load. That is what the ONAN and ONAF ratings on a nameplate describe.

Please log in or register to report this question.

Answer: D

Cast resin or open ventilated construction avoids the fire risk and the maintenance of oil, which suits indoor and building installations. Ratings and voltages are more limited than for an oil-filled unit of the same size.

Please log in or register to report this question.

79.

The efficiency of a transformer is higher than that of a rotating machine of the same rating because it has

Answer: A

Correct answer: no friction, windage or rotor loss

A transformer is static. It has copper loss and core loss like any machine, but nothing rotates, so there is no bearing friction, no windage and no rotor loss, and the cooling requirement is correspondingly smaller. That absence is the whole of the difference, and it is why transformer efficiency exceeds 99 per cent while a motor of the same rating reaches perhaps 95.

Please log in or register to report this question.

Answer: B

Connecting one end of each winding together and measuring across the free ends shows whether the emfs add or oppose, which is subtractive or additive polarity. Getting it wrong when paralleling two units is a short circuit.

Please log in or register to report this question.

Loading…
Tags: Transformers Questions and Answers || Transformers MCQ Questions and Answers || Transformers GK Questions and Answers || Transformers GK MCQ Questions || Transformers Multiple Choice Questions and Answers || Transformers GK || GK on Transformers || Electrical Machines Questions and Answers || Electrical Machines MCQ Questions and Answers || Electrical Machines GK Questions and Answers || GK on Electrical Machines