Transformers Questions and Answers

21.

A 100 kVA transformer with 500 W iron loss and 1,000 W full-load copper loss, at unity power factor and full load, has an efficiency of

Answer: A

Correct answer: 98.5 per cent

At full load and unity power factor the output is 100 kW and the total loss is \( 500 + 1000 = 1500 \) W: \[ \eta = \frac{100\,000}{100\,000 + 1500} = 0.985 = 98.5\ \text{per cent.} \] Note the loss goes in the denominator with the output, since input equals output plus losses - dividing by the output alone gives a figure above unity.

Please log in or register to report this question.

Answer: B

Because a distribution transformer is energised continuously but loaded for only part of the day, its iron loss runs for twenty-four hours while its copper loss runs for a few. Designing for a low iron loss is what raises the figure.

Please log in or register to report this question.

Answer: C

Iron loss is present the moment the transformer is connected, so on a lightly loaded feeder it dominates the day's energy loss. Power transformers, loaded nearer their rating for most of the time, are optimised differently.

Please log in or register to report this question.

Answer: D

Correct answer: the fall in secondary voltage from no load to full load

Regulation measures how much the secondary voltage sags when load is applied, expressed as a fraction of the no-load value. It is caused by the voltage dropped across the winding resistance and, more importantly, the leakage reactance. A low regulation means a stiff supply, which is why distribution transformers are designed for a few per cent.

Please log in or register to report this question.

25.

At which kind of load does a transformer show the greatest fall in its secondary voltage?

Answer: A

Correct answer: a lagging power factor

With a lagging load the current lags the voltage, so the drop across the leakage reactance adds almost directly to the resistive drop and the two combine to give the largest fall. At unity power factor the reactive drop is largely in quadrature and contributes less. A leading load can actually raise the secondary voltage above its no-load value, giving negative regulation.

Please log in or register to report this question.

26.

A transformer with a per unit impedance of 5 per cent supplying a unity power factor load at full load has a regulation of about

Answer: B

At unity power factor the reactive drop is in quadrature and contributes only to the second order, so the regulation is nearly the resistive component. It is a useful check on whether a regulation calculation has been done correctly.

Please log in or register to report this question.

27.

The short-circuit current of a transformer with 5 per cent impedance is about

Answer: C

The reciprocal of the per unit impedance gives the multiple, so a low impedance means a stiff supply and a large fault current. Switchgear has to be rated for that current, which is one reason impedance is not made smaller than it needs to be.

Please log in or register to report this question.

Answer: D

Correct answer: 30 degrees between primary and secondary line voltages

In a delta-star connection the primary line voltage is a phase voltage of the delta while the secondary line voltage is the difference of two star phase voltages, and the two differ in phase by 30 degrees. The shift matters when transformers are paralleled: two units must belong to the same vector group or a large circulating current will flow.

Please log in or register to report this question.

Answer: A

The neutral is what makes a four-wire distribution system possible and gives a reference for earthing and protection. A delta winding gives the closed path for triple harmonics, which is why the two are often combined.

Please log in or register to report this question.

Answer: B

Triple harmonics circulate within the delta rather than distorting the voltage or flowing in the neutral, which is why a delta winding is usual on at least one side. The winding current is \( 1/\sqrt{3} \) of the line current.

Please log in or register to report this question.

Loading…
Tags: Transformers Questions and Answers || Transformers MCQ Questions and Answers || Transformers GK Questions and Answers || Transformers GK MCQ Questions || Transformers Multiple Choice Questions and Answers || Transformers GK || GK on Transformers || Electrical Machines Questions and Answers || Electrical Machines MCQ Questions and Answers || Electrical Machines GK Questions and Answers || GK on Electrical Machines